Jeremy:


Do you have access to a thermal camera?  It may reveal heating in the
combiner.



Burnish the conductors (wires and comb).



Replace the breakers.  Labor is always more expensive than materials.



Breakers can fatigue.  Replace the breakers.



What is the Voc and Vmppt?  Consider replacing the breakers with touch-safe
fuses if the voltages even approach 150 VDC.



Make certain the combiner is not exposed to sunlight or other heat sources.



Good luck.



William



William Miller

Miller Solar

www.millersolar.com

CA License C-10 77398



*From:* RE-wrenches [mailto:[email protected]] *On
Behalf Of *All Solar via RE-wrenches
*Sent:* Thursday, April 30, 2026 9:26 PM
*To:* [email protected]
*Cc:* All Solar
*Subject:* [RE-wrenches] Combiner breakers tripping



Wrenches,

I've got a c client with an Outback PV combiner with DIN mount CBs. He's
let me know a few times that 9 of 10 , or at least 50%

of the breakers are tripping for no apparent reason. He resets, and all is
fine for a few months.



I suspect something is wrong with the array vs. the breakers needing
replaced.

What should I be looking for and checking?


The client has made sure the breaker screws are tight.

   - Off grid
   - Pole mounted array
   - Solarex 110 w Modules





Regards,


Jeremy Rodriguez

All Solar
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

Reply via email to