Re: [RE-wrenches] Retrofit NEC 690.31(D)(1) compliance to a PVC pipe stub

2026-05-21 Thread Dave Tedeyan via RE-wrenches
I'm a fan of talking to the inspector directly for their take. Explain the
situation. It seems like having 2" of PVC inside a TA and mounting a metal
jbox as low as possible and transitioning to metal from there should be
reasonable.

On Wed, May 20, 2026, 8:58 PM Jerry Shafer via RE-wrenches <
[email protected]> wrote:

> Wrenches. Conduit issue,
> If it is Unprotected then you need sch 80 but as it is going through
> concrete weed trimming is not really an issue, that is in my JHD anyway.
>
>
> On Wed, May 20, 2026, 3:42 PM Chris Sparadeo via RE-wrenches <
> [email protected]> wrote:
>
>> Not sure your exact situation, but a 230.6 argument could potentially be
>> made, as this exemption is often applied to “other than service
>> conductors”. Installed under min 2” of concrete can be considered “outside
>> of the building”.
>>
>>
>> On Wed, May 20, 2026 at 2:05 PM William Miller via RE-wrenches <
>> [email protected]> wrote:
>>
>>> I had a similar problem with PVC pre-installed through a roof. It was
>>> big enough pipe to run flex through and pull our PV runs.
>>>
>>> As to the requirement to use metallic, I haven’t had my second cup of
>>> coffee yet so I won’t comment.
>>>
>>> William Miller
>>> Miller Solar.com
>>> 805-438-5600
>>> www.millersolar.com
>>>
>>> On Wed, May 20, 2026 at 10:36 AM Mick Abraham via RE-wrenches <
>>> [email protected]> wrote:
>>>
 Hi, Mechanics ~

 The general contractor put in a 2" PVC pipe before pouring the slab.
 The pipe has a 90 degree sweep so there's a vertical pipe stub.
 He thought there would be no code inspections for this remote
 property... oops.

 I now must use this plastic pipe for incoming PV wires. These wires
 will terminate on a MidNite Power MN15‑12KW‑AIO, so question one:
 Without embarrassing myself, can I argue that this qualifies for the
 exemption as a PV ICS (Photovoltaic Integrated Control System)?
 The PV arrays will be on top of an open horse shed, so I don't plan on
 any form of "rapid shutdown".

 Assuming that the above exemption won't get me off the hook, what are
 your suggestions for retrofit? My five wires could comfortably fit 1" trade
 size EMT
 conduit. If I cut the PVC stub then glue on a male adapter (so I could
 mount a metal box low to the floor), there's still some unprotected plastic
 due to the hub of the male adapter.

 Also: what would have been better initial tradecraft in a non-retrofit
 slab situation, assuming that one wants to use PVC for most of the pipe run
 while still satisfying
 NEC 690.31(D) (1)?

 Thanks in advance, Mechanix. "The Wrench List is the Bomb!"

 Mick Abraham, Proprietor
 www.abrahamsolar.com

 Cell phone or for text messaging: 970-946-6584
 ___
 List sponsored by Redwood Alliance

 Pay optional member dues here: http://re-wrenches.org

 List Address: [email protected]

 Change listserver email address & settings:
 http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

 There are two list archives for searching. When one doesn't work, try
 the other:
 https://www.mail-archive.com/[email protected]/
 http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

 List rules & etiquette:
 http://www.re-wrenches.org/etiquette.htm

 Check out or update participant bios:
 http://www.members.re-wrenches.org

 ___
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>

Re: [RE-wrenches] Retrofit NEC 690.31(D)(1) compliance to a PVC pipe stub

2026-05-20 Thread Jerry Shafer via RE-wrenches
Wrenches. Conduit issue,
If it is Unprotected then you need sch 80 but as it is going through
concrete weed trimming is not really an issue, that is in my JHD anyway.


On Wed, May 20, 2026, 3:42 PM Chris Sparadeo via RE-wrenches <
[email protected]> wrote:

> Not sure your exact situation, but a 230.6 argument could potentially be
> made, as this exemption is often applied to “other than service
> conductors”. Installed under min 2” of concrete can be considered “outside
> of the building”.
>
>
> On Wed, May 20, 2026 at 2:05 PM William Miller via RE-wrenches <
> [email protected]> wrote:
>
>> I had a similar problem with PVC pre-installed through a roof. It was big
>> enough pipe to run flex through and pull our PV runs.
>>
>> As to the requirement to use metallic, I haven’t had my second cup of
>> coffee yet so I won’t comment.
>>
>> William Miller
>> Miller Solar.com
>> 805-438-5600
>> www.millersolar.com
>>
>> On Wed, May 20, 2026 at 10:36 AM Mick Abraham via RE-wrenches <
>> [email protected]> wrote:
>>
>>> Hi, Mechanics ~
>>>
>>> The general contractor put in a 2" PVC pipe before pouring the slab. The
>>> pipe has a 90 degree sweep so there's a vertical pipe stub.
>>> He thought there would be no code inspections for this remote
>>> property... oops.
>>>
>>> I now must use this plastic pipe for incoming PV wires. These wires will
>>> terminate on a MidNite Power MN15‑12KW‑AIO, so question one:
>>> Without embarrassing myself, can I argue that this qualifies for the
>>> exemption as a PV ICS (Photovoltaic Integrated Control System)?
>>> The PV arrays will be on top of an open horse shed, so I don't plan on
>>> any form of "rapid shutdown".
>>>
>>> Assuming that the above exemption won't get me off the hook, what are
>>> your suggestions for retrofit? My five wires could comfortably fit 1" trade
>>> size EMT
>>> conduit. If I cut the PVC stub then glue on a male adapter (so I could
>>> mount a metal box low to the floor), there's still some unprotected plastic
>>> due to the hub of the male adapter.
>>>
>>> Also: what would have been better initial tradecraft in a non-retrofit
>>> slab situation, assuming that one wants to use PVC for most of the pipe run
>>> while still satisfying
>>> NEC 690.31(D) (1)?
>>>
>>> Thanks in advance, Mechanix. "The Wrench List is the Bomb!"
>>>
>>> Mick Abraham, Proprietor
>>> www.abrahamsolar.com
>>>
>>> Cell phone or for text messaging: 970-946-6584
>>> ___
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: [email protected]
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/[email protected]/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
ht

Re: [RE-wrenches] Retrofit NEC 690.31(D)(1) compliance to a PVC pipe stub

2026-05-20 Thread Chris Sparadeo via RE-wrenches
Not sure your exact situation, but a 230.6 argument could potentially be
made, as this exemption is often applied to “other than service
conductors”. Installed under min 2” of concrete can be considered “outside
of the building”.


On Wed, May 20, 2026 at 2:05 PM William Miller via RE-wrenches <
[email protected]> wrote:

> I had a similar problem with PVC pre-installed through a roof. It was big
> enough pipe to run flex through and pull our PV runs.
>
> As to the requirement to use metallic, I haven’t had my second cup of
> coffee yet so I won’t comment.
>
> William Miller
> Miller Solar.com
> 805-438-5600
> www.millersolar.com
>
> On Wed, May 20, 2026 at 10:36 AM Mick Abraham via RE-wrenches <
> [email protected]> wrote:
>
>> Hi, Mechanics ~
>>
>> The general contractor put in a 2" PVC pipe before pouring the slab. The
>> pipe has a 90 degree sweep so there's a vertical pipe stub.
>> He thought there would be no code inspections for this remote property...
>> oops.
>>
>> I now must use this plastic pipe for incoming PV wires. These wires will
>> terminate on a MidNite Power MN15‑12KW‑AIO, so question one:
>> Without embarrassing myself, can I argue that this qualifies for the
>> exemption as a PV ICS (Photovoltaic Integrated Control System)?
>> The PV arrays will be on top of an open horse shed, so I don't plan on
>> any form of "rapid shutdown".
>>
>> Assuming that the above exemption won't get me off the hook, what are
>> your suggestions for retrofit? My five wires could comfortably fit 1" trade
>> size EMT
>> conduit. If I cut the PVC stub then glue on a male adapter (so I could
>> mount a metal box low to the floor), there's still some unprotected plastic
>> due to the hub of the male adapter.
>>
>> Also: what would have been better initial tradecraft in a non-retrofit
>> slab situation, assuming that one wants to use PVC for most of the pipe run
>> while still satisfying
>> NEC 690.31(D) (1)?
>>
>> Thanks in advance, Mechanix. "The Wrench List is the Bomb!"
>>
>> Mick Abraham, Proprietor
>> www.abrahamsolar.com
>>
>> Cell phone or for text messaging: 970-946-6584
>> ___
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: [email protected]
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/[email protected]/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Re: [RE-wrenches] Retrofit NEC 690.31(D)(1) compliance to a PVC pipe stub

2026-05-20 Thread William Miller via RE-wrenches
I had a similar problem with PVC pre-installed through a roof. It was big
enough pipe to run flex through and pull our PV runs.

As to the requirement to use metallic, I haven’t had my second cup of
coffee yet so I won’t comment.

William Miller
Miller Solar.com
805-438-5600
www.millersolar.com

On Wed, May 20, 2026 at 10:36 AM Mick Abraham via RE-wrenches <
[email protected]> wrote:

> Hi, Mechanics ~
>
> The general contractor put in a 2" PVC pipe before pouring the slab. The
> pipe has a 90 degree sweep so there's a vertical pipe stub.
> He thought there would be no code inspections for this remote property...
> oops.
>
> I now must use this plastic pipe for incoming PV wires. These wires will
> terminate on a MidNite Power MN15‑12KW‑AIO, so question one:
> Without embarrassing myself, can I argue that this qualifies for the
> exemption as a PV ICS (Photovoltaic Integrated Control System)?
> The PV arrays will be on top of an open horse shed, so I don't plan on any
> form of "rapid shutdown".
>
> Assuming that the above exemption won't get me off the hook, what are your
> suggestions for retrofit? My five wires could comfortably fit 1" trade size
> EMT
> conduit. If I cut the PVC stub then glue on a male adapter (so I could
> mount a metal box low to the floor), there's still some unprotected plastic
> due to the hub of the male adapter.
>
> Also: what would have been better initial tradecraft in a non-retrofit
> slab situation, assuming that one wants to use PVC for most of the pipe run
> while still satisfying
> NEC 690.31(D) (1)?
>
> Thanks in advance, Mechanix. "The Wrench List is the Bomb!"
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com
>
> Cell phone or for text messaging: 970-946-6584
> ___
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: [email protected]
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/[email protected]/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
___
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: [email protected]

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/[email protected]/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org