Thanks Chuck.

We expect depending on which site to have between a 3 amp and 5 amp load. Have 
not settled on the Ah of batteries yet just getting started on this.

 

 

From: ch...@wbmfg.com [mailto:ch...@wbmfg.com] 
Sent: Saturday, June 16, 2018 10:36 AM
To: Brandon Yuchasz; af@af.afmug.com
Subject: Re: [AFMUG] building our own 48volt DC sites grid tied.

 

Any telecom charger/rectifier will last for 20 years easy.

What kind of load amps do you need to run?  How big are the batts?

 

Your rectifier needs to be able to pull the full load current plus the heavy 
battery recharge current when the power comes back on.  Having one that limits 
current is good.  Say you have a 5 amp load current and a 100 Ah battery, you 
are going to have a minimum of 10 amps of battery charge current after an 
outage.  Probably more like 20.  So a 25 amp rectifier to run a 5 amp load plus 
batts would not be out of question.  

 

I like eltek/valere modular units.  

 

From: Brandon Yuchasz 

Sent: Saturday, June 16, 2018 9:27 AM

To: af@af.afmug.com 

Subject: [AFMUG] building our own 48volt DC sites grid tied.

 

 

 

After finally diving into our first 48 volt solar site last year we are now 
looking to convert some of our more critical sites to 48 volt battery banks 
that are still grid tied for charging the systems.  The plan being to extend 
the run time on the sites when we lose power.  Would anyone that is doing this 
type of system be willing to share some sources for the chargers that have 
stood the test of time in your network?  I am seeing these sites as 4 12 volt 
deep cycles ( or if room allows 8 – 6 volt ) this battery bank will feed new 
Packetflux Rack injectors, and the battery banks will be kept topped off by the 
charge controller. 

 

Thanks everyone,

 

Brandon

 