Our J series are isolated from the chassis unless you bond ground to the
positive ground on it.  That being said, the fuses are on the - side so you
would want to take the main outputs to your own distribution panel or bus
with the fuses on the + leg if you were going to run it at +48



On Tue, Nov 27, 2018 at 1:13 AM TJ Trout <[email protected]> wrote:

> I get it now, the 48v never changes just the ground reference.
>
> I'm guessing the reason no one uses negative ground loads on a -48 system
> is the chassis ground being bonded to the inputs return.
>
> Could I therically isolate my eltek -48 from any ground and operate it as
> a negative ground system?
>
> Or if the chassis isn't bonded to either can I just avoid grounding the
> supply?
>
> On Mon, Nov 26, 2018, 10:29 PM TJ Trout <[email protected] wrote:
>
>> Chuck,
>>
>> Are you sure the eltek's don't have the chassis ground bonded to the
>> positive output ?
>>
>> So I'm assuming the complication here is that if you reverse the wires,
>> when you try to power a +48v device, and it's negative input is bonded to
>> chassis ground and you have a ground path between the two (like a metal
>> rack) or possibly somehow through the AC ground/neutral you cause a direct
>> short circuit?
>>
>> I see mentions of DC-DC converters, but I don't see the point of using a
>> 300w RSD converter with a 2000W rectifier shelf?
>>
>>
>>
>> On Mon, Nov 26, 2018 at 2:57 PM <[email protected]> wrote:
>>
>>> It is 48.  Period.  You choose the reference if you want one.
>>>
>>> If you tie the + terminal to chassis ground then the – terminal is the
>>> hot –48 VDC terminal.
>>>
>>> If you tie the – terminal to chassis ground then the + terminal is the
>>> hot +48 VDC terminal.
>>>
>>> If you don’t tie either to chassis ground, then you will have to have a
>>> common return bar that is on the opposite rail from your fuses and circuit
>>> breakers.
>>>
>>> *From:* TJ Trout
>>> *Sent:* Monday, November 26, 2018 3:40 PM
>>> *To:* AnimalFarm Microwave Users Group
>>> *Subject:* [AFMUG] Eltek Valere J series -48 or +48
>>>
>>> I'm looking at the Valere series and I can't seem determine if it's +48
>>> or -48, seems like it's +48 but I thought all the telecom stuff was
>>> positive ground.
>>>
>>> How do you go about powering negative ground loads from a positive
>>> ground power source?
>>>
>>> I'm assuming you can leave out the neutral and isolate the chassis?
>>>
>>>
>>>
>>> ------------------------------
>>> --
>>> AF mailing list
>>> [email protected]
>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>> --
>>> AF mailing list
>>> [email protected]
>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>>
>> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>


-- 

Carl Peterson

*PORT NETWORKS*

401 E Pratt St, Ste 2553

Baltimore, MD 21202

(410) 637-3707
-- 
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com