Thanks everyone. I was a bit confused about the breaker curves as well.
I'm actually using these between a DC/DC converter and the devices being
powered from it. Was hoping to protect the converter in the event of a
short on one of the devices.

On Friday, December 28, 2018, Ken Hohhof <[email protected]> wrote:

> Are you talking the AC or DC voltage rating?  DC rating is usually lower,
> because it is harder to quench the arc when opening the circuit if the
> polarity doesn’t alternate.  It’s usually difficult to find breakers with a
> DC rating higher than 48 volts.  But a higher voltage rating is not a
> problem, just may cost a little more.
>
>
>
> You also need to look at the trip curve for the family of breakers.  The
> Altech/Sursum DIN rail breakers I usually use are not technically DC
> breakers, but they come in a bazillion different trip curves, I usually buy
> B or C.  There will be a graph that shows the min/max trip time for various
> percent current over rating.  Usually that will take care of inrush unless
> you have a load that has an unusually large or long lasting inrush.  So
> something between 1 and 2 times expected load.  Let’s face it, if the load
> is 1.7 amps, you aren’t going to have a 1.7 amp breaker in your stock of
> breakers, maybe you have 2 and 5 amp breakers on hand.  In that case I’d
> probably go with the 2 amp, because 5 amps may not offer much protection,
> especially since you probably have to get to 200% of rating for it to trip
> quicky.  The exception is any kind of DC UPS that draws extra current when
> recharging the batteries, you need to allow for that, or everything will
> seem fine until the first time you are recharging the batteries after a
> power outage, and the circuit breaker trips after about 30 seconds.
>
>
>
>
>
> *From:* AF <[email protected]> *On Behalf Of *Jason McKemie
> *Sent:* Friday, December 28, 2018 9:37 AM
> *To:* AnimalFarm Microwave Users Group <[email protected]>
> *Subject:* [AFMUG] DC Breakers
>
>
>
> Do you generally size these about double the expected load?
>
>
>
> I see a lot of them rated at higher voltages than I need, will these still
> be effective?
>
-- 