I have heard from hams that running your feed line through metallic conduit 
will choke out lightning.

Sent from my iPhone

> On May 30, 2019, at 6:47 AM, Lewis Bergman <[email protected]> wrote:
> 
> Chuck is better on the theory, I have only been to a few R56 classes so I 
> could be incorrectly remebering. The theory, again not my thing, is rooted in 
> inductance and choke which increases resistence along the length of the cable 
> traveling through the conduit. The faster the spike (strike) the greater the 
> resistance. It can cause a conductor to blow apart. it applies to a conductor 
> carrying a large surge. It has to do with the magnetic properties of all 
> ferrous metals. According to the NEC, which the R56b standard pulls from in 
> part is below and says you have to ground each end. I don't know if this is 
> the exact language in the current NEC as I don't own a copy.
> 
> NEC Section 250.64(E) includes requirements to address such protection. If a 
> grounding electrode conductor is installed in a ferrous metal raceway, the 
> raceway must be electrically continuous from the point of attachment to the 
> cabinet or equipment to the grounding electrode and must be securely fastened 
> to the ground clamp or fitting. Ferrous metal raceways contain iron or steel 
> content, and examples include rigid metal conduit (RMC), intermediate metal 
> conduit (IMC) and electrical metallic tubing (EMT). These conduits and tubing 
> have a magnetic property that reacts to rising and falling magnetic fields 
> present in alternating current (AC) systems.
> Here are some examples:
> https://www.carelient.com/2018/12/21/grounding-electrode-conductor-nec-violation-example/
>  
> https://www.ecmag.com/section/codes-standards/guardian-ground
> 
> I think I have previosuly posted a link to my dropbox with the R56. I am 
> positive it is out of date but following it is better than not following 
> anything. It has a lot of good illustrations and pictured to help clarify 
> things as well.
> Here it is again: R56 manual
> 
> The long and short of it is that is a lot easier to use PVC than ground each 
> end of the metal conduit.
> 
>> On Wed, May 29, 2019 at 10:10 PM Jaime Solorza <[email protected]> 
>> wrote:
>> Hum..the number 6 ground cable is insulated...direct bonding to 10 ft. 
>> ground rod.
>> Please explain your observation...I have had great success with this method 
>> but open to improvements or corrections 
>> Thanks
>> 
>>> On Wed, May 29, 2019, 9:02 PM Lewis Bergman <[email protected]> wrote:
>>> That conduit might serve as a choke on that ground.
>>> 
>>>> On Wed, May 29, 2019, 9:56 PM Jaime Solorza <[email protected]> 
>>>> wrote:
>>>> Site pro mount, PC-Tel antenna, Heliax cable and accessories. .inside 
>>>> GE-MDS radio. 928.xxx and 952.xxx MHz.
>>>> -- 
>>>> AF mailing list
>>>> [email protected]
>>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>>> -- 
>>> AF mailing list
>>> [email protected]
>>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>> -- 
>> AF mailing list
>> [email protected]
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
> 
> 
> -- 
> Lewis Bergman
> 325-439-0533 Cell
> -- 
> AF mailing list