Large stationary C.O. battery ratings are 80% dod.

Sent from my iPhone

> On Nov 7, 2020, at 8:03 PM, Robert <[email protected]> wrote:
> 
>  But you want to only take a lead battery to 1/2 that to avoid decreasing 
> the longevity of them, so double the battery size and, if the batteries are 
> going to be outside in the winter you will lose performace so double it again.
> 
> Lithium, I have learned that yes you can discharge them fully but you only 
> want to charge them to 80% to get maximum life.   So you only need to go 120% 
> of your battery calculation for lithium...
> 
> 
> 
> On 11/7/20 1:40 PM, [email protected] wrote:
>> 30 watts * 24 *14 = approx 10 kWh.  So you need a 10 kWh battery.  10 kWh/48 
>> = 210 Ah 48 volt battery.
>>  
>> Now, I have lotsa experience at my latitude and weather.  I will take a stab 
>> at your situation.  If you can easily get a generator to the site it makes a 
>> huge difference. 
>>  
>> I would say you need a minimum of 300 watts of panel which is not much.  You 
>> can get one single panel of that size.  Depending on the type of charge 
>> controller you use, you will probably want 2 or 3 panels to get the voltage 
>> up in the 60-100 volt range. 
>>  
>> So take a look at the MMPV of the panels you choose and add them up in 
>> series.  Take a look at the max input voltage of your charge controller.  
>> Try to get the series voltage of the panels close to that max input voltage 
>> if you can. 
>>  
>> I promise it will work if you do 600 watts of panel, that would be at my 
>> latitude, middle of winter with snow and storms.  20X the load is my rule of 
>> thumb here for off grid.  20X the load and 2 weeks of battery autonomy saves 
>> you from expensive helicopter rides in the middle of winter.  So that is why 
>> I am recommending 10X for you.  I think Bill once said he can get by with 
>> 10X down where he lives. 
>>  
>> From: Gino A. Villarini
>> Sent: Saturday, November 7, 2020 12:13 PM
>> To: AnimalFarm Microwave Users Group
>> Subject: [AFMUG] Solar calculator?
>>  
>> Anyone with a good online calculator?
>>  
>> Or can you assits with:
>>  
>> What size of panel and batteries would I need for a 48v 30W setup to run 
>> 24/7 for at least 14 days without power?
>> Gino Villarini 
>> Founder/President
>> @gvillarini
>> t: 787.273.4143 Ext. 204 
>>                                                      
>> www.aeronetpr.com | Metro Office Park #18 Suite 304 Guaynabo, PR 00968
>> 
>> -- 
>> AF mailing list
>> [email protected]
>> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>> 
>> 
> 
> -- 
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
-- 
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com