(dumb question but sometimes they are the easy fix) are you doing the little silver screw to turn them on? Also reseat them firmly then turn them on.
We had dozens of the 80kw's running here and have been migration the to monster 500KW setups lately. -----Original Message----- From: AF <[email protected]> On Behalf Of Nate Burke Sent: Tuesday, January 03, 2023 12:11 PM To: AnimalFarm Microwave Users Group <[email protected]> Subject: [AFMUG] Symmetra UPS Questions I have a server room that has a Symmetra PX 20kw that I inherited. On the 25th it reported that 2 of the 3 10kw Power modules went bad. I ordered 2 new 10kw power units, and when i put them in, now all 3 power modules are report 'Off & OK' with a green check mark. They battery system is reporting 'OK' but I'm wondering if the batteries might be causing a problem. Will the power modules not start if the batteries are bad? There is about 9kw of load on the UPS. The battery system says Nominal voltage is 192v, but actual voltage is 154v. When we measure each pack it's at 96v. and 2x96 should be 192, so it must need a minimum of 2 packs to work. -- AF mailing list [email protected] http://af.afmug.com/mailman/listinfo/af_af.afmug.com -- AF mailing list [email protected] http://af.afmug.com/mailman/listinfo/af_af.afmug.com