I have an MPS Ultra with a temperature probe.  Using SNMP and our billing
system Vision.  I like to make sure that's 77* give or take 10*.

At the end of the day if that temperature (the bottom value on the sheet)
is the concern - if there's an issue with the AC unit, too much/little
heat, people leaving the door open, etc it's all summed up in that one
value.

On Tue, May 27, 2025 at 3:35 PM Adam Moffett <[email protected]> wrote:

> Does anyone here monitor air conditioners?  If so, how do you do it?
>
> Up until now, I would find out about an A/C failure by getting temperature
> alarms from equipment.  When I look at the chart of temperature over time
> it usually looks the A/C fail happened hours (sometimes many hours) before
> the temperature got critical.  It'd be nice to respond sooner.
>
>
>    - My first and cheapest idea was to run another temperature sensor
>    from the rectifier and attach it to the output vent of the air
>    conditioner.  I'd trigger an alarm when that exceeds some threshold, say
>    80F or 85F.
>
>
>
>    - I also looked at fancy controllers with Ethernet and SNMP
>    that'll alert you when the filter is clogged, or detect refrigerant leaks,
>    or whatever.   But these all seem to be vendor specific.
>
>
>
>    - Bard makes a couple of Ethernet enabled lead-lag controllers that
>    are generic enough that I could connect them to any A/C unit with terminals
>    for an external thermostat, but these are very limited as to what alarms
>    you'll get.  High and low temp alarms, and probably an alarm if the A/C
>    unit is off completely.....which is not a common failure mode in my
>    experience.  Basically if you're not adding lead-lag functionality a
>    generic solution doesn't get much any new info.
>
>
> Are there options I'm overlooking?  I know mostly nothing about Modbus
> over TCP for example....would that do anything for me?
>
> I actually am pushing for redundant lead-lag systems at new sites, and I
> can get the controller that goes with those systems.  For existing
> installations I'm thinking the extra temperature sensor is the most
> sensible thing.  Is there a better way that I'm overlooking?
>
>
> --
> AF mailing list
> [email protected]
> http://af.afmug.com/mailman/listinfo/af_af.afmug.com
>
-- 
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to