I once created a telemetry/alarm combo for supermarket freezers and =
residential HVAC.  It had two sensors.  I think they want across the =
evaporator.  I do know that measuring superheat was the key.  I never =
really understood what that meant but it was a key factor in determining =
the health of the system.  It was for an insurance company.  Hartford =
Steam Boiler Company.  Enron bought them and I never got another order.  =


-----Original Message-----
From: AF [mailto:[email protected]] On Behalf Of Seth Mattinen via =
AF
Sent: Thursday, June 12, 2025 11:44 AM
To: [email protected]
Cc: Seth Mattinen <[email protected]>
Subject: Re: [AFMUG] Air Conditioner Monitoring

On 5/27/25 12:34, Adam Moffett wrote:
> Does anyone here monitor air conditioners?  If so, how do you do it?
>=20
> Up until now, I would find out about an A/C failure by getting=20
> temperature alarms from equipment.  When I look at the chart of=20
> temperature over time it usually looks the A/C fail happened hours=20
> (sometimes many hours) before the temperature got critical.  It'd be=20
> nice to respond sooner.


One simple thing to start with is take two temperature sensors and place =
one in the air stream before the coil and one after the coil. If the air =
temperature drop is less than 20 degrees F while it's running in cooling =
mode, you are going to have a problem soon.

Getting a little fancier: tap all of the thermostat wires and contactors =
so you can read all of the control wiring states. i.e. if the tstat is =
calling for cooling but the compressor contactor is still de-energezed, =
you have a problem.

Adding a differential pressure switch across the blower can detect =
blower motor failures and/or weak airflow depending how sensitive it is.