I won’t comment on the issue of how nice it should look for the price you paid.

 

But in my mind, that is a restricted access location, so inside the enclosure 
you don’t need wires run in conduit and stuff like that.  You could put a sign 
on the door something like authorized personnel only.  But when we build out 
our own enclosures, we don’t worry if breakers and fuse blocks and power 
supplies on the DIN rail have exposed terminals, even if they are 120 or 240 
VAC or 48 VDC, and we don’t worry about exposed battery terminals.  We will 
bring power into the enclosure via conduit using THHN , and we might put a 
handibox on the enclosure backplate for AC outlets, but won’t run that THHN in 
conduit.  We’ll use a chase nipple on the handibox.  Same with AC to enclosure 
fans, it would be silly to try and put those in conduit inside an enclosure.

 

What I worry more about with THHN stranded electrical wire is it doesn’t get 
along with a lot of the compression terminals on DIN rail equipment like power 
supplies.  So I end up crimping ferrules onto the wires, but that can come with 
its own set of issues.

 

From: AF <[email protected]> On Behalf Of Adam Moffett
Sent: Monday, February 16, 2026 3:38 PM
To: AnimalFarm Microwave Users Group <[email protected]>
Subject: Re: [AFMUG] THHN in Wire loom

 

Fiber.

 

And I dug into it a bit more.  The enclosure is actually made by Vertiv.  
Vertiv sells it with a load center, and they have a battery heater and GFCI 
outlet prewired.  The items prewired by Vertiv have liquitite conduit going to 
them.  An integrator working for Nokia would have installed the rectifier and 
did the wire loom thing.  I'm not sure how well that squares with the "inside 
of an appliance" notion.  

 

Vertiv's instructions point an arrow at the same 3/4" knockout for AC input.  I 
think we're just not supposed to have a 100A breaker.  Nokia should talk to 
their integrator.

 

-Adam

 

 

  _____  

From: AF <[email protected] <mailto:[email protected]> > on behalf 
of Mark Radabaugh <[email protected] <mailto:[email protected]> >
Sent: Monday, February 16, 2026 2:35 PM
To: AnimalFarm Microwave Users Group <[email protected] <mailto:[email protected]> >
Subject: Re: [AFMUG] THHN in Wire loom 

 

Drinking the Nokia cool-aid eh?    Fiber or LTE? 

 

Mark

 

On Feb 16, 2026, at 11:45 AM, Adam Moffett <[email protected] 
<mailto:[email protected]> > wrote:

 

If the AC and DC wiring are kept compartmentalized, then I think that's true. 
The AC power components are kept physically separated, so when you open the 
machine for maintenance you have to open some separate compartment or open 
another box to get into the AC stuff.  It's like that in appliances, computers, 
and most machines. 

 

I guess someone at Nokia must have looked at this and decided it was all ok, 
but I don't like it.  If I cobbled it together myself, it would have come out 
better than this. 

 

<image.png>

 

  _____  

From: AF <[email protected] <mailto:[email protected]> > on behalf 
of Chuck <[email protected] <mailto:[email protected]> >
Sent: Friday, February 13, 2026 9:51 PM
To: [email protected] <mailto:[email protected]>  <[email protected] 
<mailto:[email protected]> >
Cc: [email protected] <mailto:[email protected]>  <[email protected] 
<mailto:[email protected]> >
Subject: Re: [AFMUG] THHN in Wire loom

 

As a manufactured “appliance” I don’t think the NEC applies to anything inside 
the box.

Sent from my iPhone

 

On Feb 13, 2026, at 4:52 PM, Adam Moffett <[email protected] 
<mailto:[email protected]> > wrote:



This post is part question and part whining.

 

Yesterday I got a look at a manufactured network enclosure from a fairly large 
company.  They have a load center built in, and the feeds to the rectifier are 
THHN in wire loom.  They bring that into the load center with NM box 
connectors.  

 

I want to believe that they wouldn't sell something to us for $30,000 that 
wasn't up to electrical code, but 

1.      I have never seen that done before, and neither has our electrician

2.      It doesn't make me feel like I got $30,000 worth

 

Does anyone know if this is actually square with the NEC?

 

Even if it's legally ok, how does it make any sense?

 

<image.png>

 

<image.png>

 

 

Weird thing #2:

 

The installation guide says to bring our incoming utility power through the 
knockout shown here under the load center.  The one next to it with the rubber 
passthrough is for a ground to the equipment MGB.  It's a ¾ knockout, and I 
added a picture of the bottom side to show that it's not one of the expandable 
ones.  The main breaker in the load center is 100A. Normally you'd want a 1-1/4 
knockout for a 100A service.  I struggled to think of some creative way to get 
100A through a ¾ conduit and still be compliant, but I got nothing.  I think 
we'll have to remove the factory breaker and install a 50A.  It's either that 
or bore a 1.7" dia hole somewhere, and while I do enjoy cutting up metal I 
don't think I should have to.

 

<image.png>

 

<image.png>

 

--
AF mailing list
[email protected] <mailto:[email protected]> 
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

--
AF mailing list
[email protected] <mailto:[email protected]> 
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

 

-- 
AF mailing list
[email protected]
http://af.afmug.com/mailman/listinfo/af_af.afmug.com

Reply via email to