Ok cool. Not too concerned with current just wanted to make sure there was
no reason each supply couldn't still function normally once in a series
configuration.
On Mar 14, 2015 12:30 PM, "Chuck McCown" <[email protected]> wrote:

>   For example, if you had a 2 amp limitation of the first 12 volt power
> supply but 10 amps for all the others, and you connected a load at the 36
> volt points that drew 2 amps, you cannot connect any other loads.
>
>  *From:* TJ Trout <[email protected]>
> *Sent:* Saturday, March 14, 2015 1:26 PM
> *To:* [email protected]
> *Subject:* Re: [AFMUG] Power supplies in series
>
>
> So I should be able to connect 12 24 36 and 48 devices to the string as
> long as the sum of my wattage doesn't exceed the psu total wattage
> On Mar 14, 2015 12:09 PM, "Mark Radabaugh" <[email protected]> wrote:
>
>> On 3/14/15 2:50 PM, TJ Trout wrote:
>>
>>>
>>> I have 4 12v power supplies with isolated outputs that I plan to put in
>>> series to make 48v but I was wondering is it possible to still connect to
>>> only one or two while they are all in series to be able to draw 12, 24, and
>>> 48v? Or once they are on series you can't use anything but the total output
>>> ?
>>>
>>>
>> If they are in series the available current is the current rating of the
>> smallest power supply.   If all of these are the same and can put out 2
>> amps each than the total string is capable of 2 Amps.
>>
>> If you asking if you can pull off different voltages along the chain, say
>> some +12, some +24, maybe +36 and +48 the answer is yes - but the current
>> limit is 2 Amps for everything combined.
>>
>> Mark
>>
>> --
>> Mark Radabaugh
>> Amplex
>>
>> [email protected]  419.837.5015 x 1021 <419.837.5015%20x%201021>
>>
>>

Reply via email to