I would go with your first plan of bonding your cabinet to the electrical 
ground / steel conduit versus adding a grounding rod.   I think you are going 
to be better off not having a secondary ground path.

Mark


> On Jun 24, 2015, at 5:53 PM, That One Guy /sarcasm 
> <[email protected]> wrote:
> 
> We have a new pop going up im putting the enclosure in tommorrow.
> 
> We get our power from a secondary distribution panel on the leg. This penel 
> is not directly grounded locally, there is metal conduit going into the 
> ground where it gets its feed from the primary somewhere else. There is a 4 
> o6 6 guage copper ground that their panel in the secondary distrubution is 
> bonded to, I assume it terminates on the other end of the conduit at the 
> main. 
> 
> We just have a 15 amp breaker in there feeding over to our enclosure via some 
> non metalic liquid tight. The ground is bonded to our enclosure bond. This is 
> only 14 guage stranded (its like 6 feet)
> 
> Im figuring at minimum I need to run a bonding wire over and attach to their 
> copper.
> 
> What I dont know is if I am doing more harm than good by putting in a ground 
> rod as well for our enclosure. I can make no site changes, and the site 
> manager doesnt know anything about it so doing it "right" really isnt an 
> option here.
> 
> I just need to know whether its potentially worse to have my enclosure on a 
> fresh ground rod potentially making our enclosure a good path for them, If I 
> place the ground rod between or enclosure and their copper I would at least 
> be isolating our enclosure, but have the potential for causing issues for 
> them.
> 
> -- 
> If you only see yourself as part of the team but you don't see your team as 
> part of yourself you have already failed as part of the team.