One of the fun things you will see if you visit eastern WA is the Yahoo
Chicken Coop design datacenter:

https://gigaom.com/2010/09/19/now-online-yahoos-chicken-coop-inspired-green-data-center/

http://www.datacenterknowledge.com/archives/2011/12/12/inside-yahoos-chicken-coop-data-center/

http://www.datacenterknowledge.com/archives/2013/03/25/yahoo-building-a-bigger-computing-coop/

During most of the winter they use massive squirrel cage blowers & filters
to bring in outside air. Quincy, WA stays nice and cold from October-March.


On Mon, Sep 28, 2015 at 10:43 AM, Nate Burke <[email protected]> wrote:

> I'm looking to add backup cooling to a small computer room, <200sqft.
> Primary cooling is via a RTU (roof top unit), but I can't put that on our
> generator (240v genset vs 480v RTU).  I'm thinking like a 2 or 3 ton Split
> system would be perfect.  Problem is we're in the midwest, and outdoor
> temperatures can drop to 0 or below over the winter.  Looking at the split
> systems, nobody seems to know if they will work for cooling with outdoor
> temperatures that low.  Online searching has yielded results for Heat Pump
> units, where they want to Heat with low temperatures.  Has anyone had
> experience with Split systems cooling with low outdoor temperatures?  Are
> there special compressors built for that use?  I have heard about putting a
> thermostat on the fan line to cut out the compressor fan below ambient X
> temp, or shrouding the compressor to keep wind from blowing through it.
> But have not been able to confirm from any HVAC contractor the validity.
>
> This would only be for backup use, RTU Failure, or power outage. The RTU
> is handling the load normally without an issue.  My Current Backup is
> Movincool units, but I want to reclaim the floor space, and make it more
> permanent.
>
>
>

Reply via email to