Do you already have the fiber?  If not, you should consider a hybrid cable
that has a few strands of fiber and 2-conductor 12/14AWG for powering the
radios?  Best-Tronics is a good vendor for this cable.

On Tue, Dec 1, 2015 at 4:11 PM, Craig Baird <cr...@xpressweb.com> wrote:

> We've got some Cambium PTP820S radios going up shortly.  We will be
> running fiber to the radios, so we're debating on POE vs. DC up the tower
> for powering them.  We have been told by the tower owner that we need to
> adhere to R56 for lightning protection.
>
> Our initial thought was that we would just run POE since we already have
> the cable, and it would give us an out-of-band management port.  But,
> according to the Cambium installation manual (and I think R56 specifies
> this too), it says that if we're running POE, we're supposed to bond the
> cable shield to the tower every 50 meters.  I assume that means at the top
> and bottom since our cable runs are all less than 50 meters. In addition,
> the manual says that we should use Ethernet surge suppressors.  We're
> thinking "what a pain in the butt".  On the other hand, the Cambium manual
> does not address grounding for DC cable in any way other than saying that
> the radio has DC (and Ethernet) surge protection built in.
>
> So the DC option is looking pretty attractive compared to the hoops we'll
> need jump through for ethernet.  I'm wondering if there's something we're
> missing that the Cambium manual doesn't address.  I figured just to be
> safe, we would go ahead and put DC surge suppressors at the top and bottom
> of the DC cable.  Is there anything else needed for R56 adherence in this
> situation?
>
> Craig
>
>
>

Reply via email to