And if I’m using AGM sealed batteries what voltage in this configuration should 
I tell the UPS to shut off?

From: Af [mailto:[email protected]] On Behalf Of Sterling Jacobson
Sent: Monday, June 13, 2016 4:37 PM
To: [email protected]
Subject: Re: [AFMUG] Peukert Number

I think if you wire in series you add the voltage, so it’s 48v right?

But the AH stays the same so I would still have 75Ah?

From: Af [mailto:[email protected]] On Behalf Of Josh Luthman
Sent: Monday, June 13, 2016 4:31 PM
To: [email protected]<mailto:[email protected]>
Subject: Re: [AFMUG] Peukert Number

If you wire 4 batteries in series that's 12v =)


Josh Luthman
Office: 937-552-2340
Direct: 937-552-2343
1100 Wayne St
Suite 1337
Troy, OH 45373

On Mon, Jun 13, 2016 at 6:27 PM, George Skorup 
<[email protected]<mailto:[email protected]>> wrote:
Does not compute. If he's running four 75ah batteries in series to get a 48VDC 
battery, then he gets 75Ah.
On 6/13/2016 5:24 PM, Josh Luthman wrote:
Oh you're complicating the question...I think.

The capacity from one 75ah is simply quadrupled in your case.  You have 300ah.  
When you add another (identical) battery you're adding capacity/runtime 
linearly.


Josh Luthman
Office: 937-552-2340<tel:937-552-2340>
Direct: 937-552-2343<tel:937-552-2343>
1100 Wayne St
Suite 1337
Troy, OH 45373

On Mon, Jun 13, 2016 at 6:23 PM, Sterling Jacobson 
<[email protected]<mailto:[email protected]>> wrote:
Yeah, the Alpha will calculate this, but I need to know how to calculate 
Peukerts Number.
Or if I’m just running a simple series of four 12v for 48  volts is 1.1 just 
the default I should use?

Do I add up all the four 75ah ratings per battery and use that as the rated 
battery capacity number at 300ah?

From: Af [mailto:[email protected]<mailto:[email protected]>] On Behalf 
Of Josh Luthman
Sent: Monday, June 13, 2016 4:20 PM
To: [email protected]<mailto:[email protected]>
Subject: Re: [AFMUG] Peukert Number

Peukert's formula, T = C / In (or C = T * In), where C is theoretical capacity 
(in amp-hours, equal to actual capacity at one amp), I is current (in amps), T 
is time (in hours), and n is the Peukert number for the battery.

http://www.csgnetwork.com/batterylifecalc.html

This?


Josh Luthman
Office: 937-552-2340<tel:937-552-2340>
Direct: 937-552-2343<tel:937-552-2343>
1100 Wayne St
Suite 1337
Troy, OH 45373

On Mon, Jun 13, 2016 at 6:18 PM, Sterling Jacobson 
<[email protected]<mailto:[email protected]>> wrote:
Been reviewing my site capacity/UPS/Batteries.

Our Alpha's have a Peukert Number to help identify and tweak capacity in 
remaining amp hours.

Can someone give me the short of this calculation?

That is, if I have four 12v batteries run in series that are 75AH each?




Reply via email to