My 2 cents.  Never assume ANYTHING about existing ground at the tower, at the 
shelter, at the service panel.  Measure everything.  If you get a sub-Ohm 
measurement you are tied into a loop which may or MAY NOT actually be 
“effectually” grounded. Remember that CADWelds can break with a strong enough 
strike, so a ground ring around in or outside of a shelter may indeed have poor 
grounds to the actual earth.  We put in inspection boxes (sprinkler boxes) at 
every connection point to be able to come back later and test.

50% of the commercial towers we tested had at least one leg of their tower 
grounds be under spec.  For us, (and the cell guys) spec is <5ohm, but if all 
points were at 8 ohm I wouldn’t freak out.  More than 50% of the electrical 
panels we pull from had poor ground.  We either forced the tower companies to 
fix the problem or if they didn’t, magically it would get fixed in the middle 
of the night.  Pays BIG dividends in Florida.

From: Af [mailto:[email protected]] On Behalf Of Justin Wilson
Sent: Friday, December 2, 2016 1:21 PM
To: [email protected]
Subject: Re: [AFMUG] CAT5e/6 tower grounding

http://wirelessestimator.com/content/standards/eia_tia_222/protective-grounding-standard

this is a good start.

https://sites.auburn.edu/admin/facilities/spw-bid-calendar/11-150%20AU%20Regional%20Airport-Construct%20a%20Self-Supporting%20Radio%20Tower/Project%20Documents/1/Motorola_R56_2005_manual.pdf



Justin Wilson
[email protected]<mailto:[email protected]>

---
http://www.mtin.net Owner/CEO
xISP Solutions- Consulting – Data Centers - Bandwidth
http://www.midwest-ix.com  COO/Chairman
Internet Exchange - Peering - Distributed Fabric

On Nov 22, 2016, at 7:54 PM, Dev 
<[email protected]<mailto:[email protected]>> wrote:

I’ve heard it’s good to ground multiple places, like up by the radio, down by 
the turn to the ice bridge and inside the shelter, but how do you that (and is 
it necessary) with CAT5e/6? Do you strip a section off the insulation and tie 
the drain wire to multiple ground lugs? Sounds hard to do and not get water in 
the cable. I just have been running surge suppressors inside the building that 
the cable plugs into before heading to the switches/etc. What should I be doing?

Reply via email to