It should not have continuity between neutral and ground.  Take a new one that 
is not connected to any wires.  An ohm meter will not show any connection.  

When installed there will be a circuit but it will flow through the neutral and 
ground wires clear back to the service entrance.  That is where the circuit 
completes.  

From: That One Guy /sarcasm 
Sent: Thursday, February 16, 2017 11:15 AM
To: [email protected] 
Subject: Re: [AFMUG] APC Site Wiring Fault

Ive never busted apart an outlet, but its got continuity between the neutral 
and ground, is the bus between the two slightly resistive like higher cost ospf 
path to keep the current on the neutral?

On Thu, Feb 16, 2017 at 12:06 PM, Chuck McCown <[email protected]> wrote:

  Except in three phase, in three phase the neutral may or may not have much 
current on it.  Sometimes it may not even exist.  

  From: Chuck McCown 
  Sent: Thursday, February 16, 2017 11:03 AM
  To: [email protected] 
  Subject: Re: [AFMUG] APC Site Wiring Fault

  The neutral and ground have totally different jobs to do.  The neutral is the 
return path and has the exact same (should be exact same) current at the hot.  
It works.

  The ground should not have any current.  It does not work.  It is a storm 
drain.  If there is a fault it conducts the fault current and helps the circuit 
breaker blow.  The only place you can treat them the same is at the service 
entrance where there is a ground rod.

  From: That One Guy /sarcasm 
  Sent: Thursday, February 16, 2017 10:46 AM
  To: [email protected] 
  Subject: Re: [AFMUG] APC Site Wiring Fault

  I did not know this about sub panels 
  I see alot of times where the electricians run the ground and neutral into 
the same hole 
  Im guessing in this case calling in that electrician to investigate wouldnt 
do alot of good
  but since theyre bonded at the service panel if they do that is it OK?

  On Thu, Feb 16, 2017 at 10:49 AM, Seth Mattinen <[email protected]> wrote:

    On 2/16/17 08:38, Chuck McCown wrote:

      But they run back to two different bars.  The neutral bar and the ground
      bar.  Then normally those two are bonded and the ground bar goes to the
      building entrance ground rod.  Any bad connection coupled with decent
      amount of current causes voltage differences.



    Bonded only at the service entrance and separate at sub-panels; that's 
important.

    Also worth considering: there was a time when separate ground conductors 
wasn't required and it was OK to use the metal conduit itself as the ground 
path. This is no longer allowed because over time conduit fittings can loosen 
and make the ground bad, possibly intermittently.

    ~Seth





  -- 