Ok, let's try this solving for Vdrop instead of Vload... See if I come up with the same solution as chuck:
For the Load: Vload=Pload/I For the resistive drop of the cable: I=Vdrop/Rcable Overall Voltage math: Vin=Vdrop+Vload Substituting Vload: Vin=Vdrop+Pload/I Substitute I: Vin=Vdrop+Pload/(Vdrop/Rcable) Simplify... And I get exactly the same formula as before.... Ahhh... the + term turns out to be the output voltage and the - term turns out to be the vdrop. Doesn't explain chuck's additional stuff at the bottom of the formula though. On Fri, Mar 10, 2017 at 5:24 PM, Forrest Christian (List Account) < li...@packetflux.com> wrote: > The generalized solution: > > For the Load: > I= Pload/Vload > > For the resistive drop of the cable: > Vdrop=Rcable*I > > Overall Voltage math: > Vin=Vdrop+Vload > > Substituting Vdrop: > Vin=Rcable*I+Vload > > Substitute I: > Vin=Rcable*(Pload/Vload)+Vload > > Now is where my math gets messy... Enter the above into microsoft math, > solve for vload, you get: > > [image: Inline image 1] > > and: > [image: Inline image 2] > > > Now some funny math to see if one or the other makes sense. Assume Rcable > to be so close to zero to be zero, what is the result? > > On the top one, setting rcable to zero, results in that term being zero, > which leaves Vin^2 alone under the square root which further simplifies to > vin. So you end up with Vload = (Vin-Vin/2). Wrong. > > The second one, same procedure results in Vin+Vin/2, or simplifies to > Vload =Vin. > > So the second one is correct for zero ohm cable drop. I'm going to guess > it's valid for all cases. Just as a simple test: > > Vload=sqrt((48*48-4(1)(1))+48)/2) > (48V in, 1 watt load, 1 ohm cable) > > Vload=(sqrt(48*48-4)+48)/2 > > Doing some math, results in a 47.97. Seems pretty accurate...... > > > > > > > On Fri, Mar 10, 2017 at 2:08 PM, Bill Prince <part15...@gmail.com> wrote: > >> Then here is what I'd do. First, assume the wire has zero resistance. >> Figure out what the dynamic resistance of the SM is at that condition. >> >> In the latest example (first example was 6 watts, now we're at 9 watts), >> the SM pulls .1875 amps. In this condition, the SM presents a 256 ohm load. >> >> Then add in the resistance of the line, and see if it is a significant >> percentage of that load. 100 ohms would be more than 1/3 of the load. >> >> If it was only 10 ohms, then no big deal. Given a big voltage drop across >> the line, it would be reasonable to assume that the SM would draw more >> current when given a lower voltage. >> >> My inclination would be to measure it rather than try to predict it when >> it's a black box. >> >> >> bp >> <part15sbs{at}gmail{dot}com> >> >> >> On 3/10/2017 11:43 AM, ch...@wbmfg.com wrote: >> >> But when you add a significant series loop resistance you cannot say >> that. The canopy SM is more of a constant power load, like the formula I >> am trying to solve. >> >> If the SM draws a constant 9 watts, I use a 24 volt power supply and I >> insert 15 ohms of cat 5 resistance, how much current will there be? >> >> *From:* Bill Prince >> *Sent:* Friday, March 10, 2017 12:41 PM >> *To:* af@afmug.com >> *Subject:* Re: [AFMUG] Fw: the solution >> >> >> It would help a lot to see what the voltage drop across the SM is. In the >> case of a Canopy SM, it's going to be about 29 volts. In which case, the >> rest of it is easy. I'm sure each type of SM or CPE has it's own power >> characteristics, so this would depend on that more than anything. >> >> >> >> bp >> <part15sbs{at}gmail{dot}com> >> >> >> On 3/10/2017 11:34 AM, ch...@wbmfg.com wrote: >> >> The load settles in at some resistance depending on what voltage it >> sees. Canopy FSK SM did the exact same thing. It would run form 10.5 to >> 24 volts and burn about 7 watts irrespective of what voltage it was >> seeing. >> >> So this calculation is important for stuff we all use. However we are >> usually not trying to put the limits of a loop resistance or voltage. I >> really don’t want to have to put 240 VDC on a twisted pair but I will if I >> have to. >> >> A general solution where you input the load power and loop resistance and >> it returns the minimum voltage is what I am trying to develop here. >> >> *From:* Bill Prince >> *Sent:* Friday, March 10, 2017 11:34 AM >> *To:* af@afmug.com >> *Subject:* Re: [AFMUG] Fw: the solution >> >> >> P=I**R >> >> (power equals current squared times resistance) >> >> The issue for this problem is that we know neither the current nor the >> "resistance" of the load, nor the voltage drop over the 100 ohm part of the >> circuit. >> >> >> >> bp >> <part15sbs{at}gmail{dot}com> >> >> >> On 3/9/2017 9:07 PM, Chuck Macenski wrote: >> >> Ok, doing software apparently has erased some important stuff from my >> brain. Hard to know what else I lost. Having said that, why is Vr = I**2 * >> R? Wouldn't Vr = I * R? >> >> On Thu, Mar 9, 2017 at 9:59 PM, Chuck McCown <ch...@wbmfg.com> wrote: >> >>> >>> As you can see, I actually arrived at the solution early on, but then >>> stumbled around searching for the linear solution which does not exist. >> >> >> >> >> >> >> > > > -- > *Forrest Christian* *CEO**, PacketFlux Technologies, Inc.* > Tel: 406-449-3345 | Address: 3577 Countryside Road, Helena, MT 59602 > forre...@imach.com | http://www.packetflux.com > <http://www.linkedin.com/in/fwchristian> <http://facebook.com/packetflux> > <http://twitter.com/@packetflux> > > -- *Forrest Christian* *CEO**, PacketFlux Technologies, Inc.* Tel: 406-449-3345 | Address: 3577 Countryside Road, Helena, MT 59602 forre...@imach.com | http://www.packetflux.com <http://www.linkedin.com/in/fwchristian> <http://facebook.com/packetflux> <http://twitter.com/@packetflux>