We use Magnum Power pure sine wave on-line UPSs with AGM batts. Yeah we
lose in the conversion, but we also don't have to fumble around with a
couple of various DC voltages.

Love them. Made in the US too.

On Jul 28, 2017 4:20 AM, "Gino A. Villarini" <[email protected]> wrote:

> Our issues is exclusively with AF24’s and APC SU750’s.  On a Switching
> event the AF24 lock up about 50% of the time.  We have been changing the
> APC750 with the newer APC SUA750 and the problem vanishes…  believe me we
> have trie everything, grounding, changing UBNT POE, Surge Suppressors, you
> name it.
>
> 2 things have only worked:
>
> Newer APC models with any POE
> Powering the the AF24 with a dc-dc converter connected to the site
> batteries and into a McCown DC injector
>
> From: Af <[email protected]> on behalf of Colin Stanners <
> [email protected]>
> Reply-To: "[email protected]" <[email protected]>
> Date: Thursday, July 27, 2017 at 9:53 PM
> To: "[email protected]" <[email protected]>
> Subject: Re: [AFMUG] Is there such a thing as a AC Capacitor?
>
> I forgot to mention:
> -if it's a non-sinewave UPS, it could be that the powersupply is designed
> to expect sinewave AC.
> -are you certain that it's not a grounding issue or other stray voltage
> between the circuits?
>
>
>
> *Gino A. Villarini*
> President
> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>
> On Thu, Jul 27, 2017 at 8:50 PM, Colin Stanners <[email protected]>
> wrote:
>
>> Gino, can you say which gear? Most UPSes switch pretty much "instantly"
>> (less than one AC cycle, which lasts 16ms) so a PSU that wouldn't last one
>> AC cycle must have very questionable engineering. Or assuming that you use
>> APC UPSes, you can change the sensitivity setting to switch quicker:
>> http://www.apc.com/us/en/faqs/FA156514/
>>
>> On Thu, Jul 27, 2017 at 2:57 PM, Gino A. Villarini <[email protected]>
>> wrote:
>>
>>> Got some  gear that hangs when UPS switches from AC power to Batts…
>>> needs something to power AC for microseconds
>>>
>>>
>>>
>>> *Gino A. Villarini*
>>> President
>>> Metro Office Park #18 Suite 304 Guaynabo, Puerto Rico 00968
>>>
>>>
>>
>

Reply via email to