GFI simply looks at the current going out on the hot wire and the current 
coming back on the neutral.  If the currents are not identical, the little 
transformer they pass through creates an output voltage that trips the unit.  
The transformer is wired such that the two currents cancel each other.  So when 
they are the same, they totally and perfectly cancel.  If more current is on 
the  hot than the neutral (or the unlikely situation where there is more on 
neutral than hot) it trips..

If it is tripping, somewhere current is leaking out of the circuit and 
returning via earth ground.  You can always put an isolation transformer on the 
output which will stop the tripping and make it safe at the same time.  Best to 
fix the leakage.  

From: Steve Jones 
Sent: Wednesday, August 02, 2017 7:29 PM
To: [email protected] 
Subject: Re: [AFMUG] Gfi kicking on portable generator

I dont know what actually is happening when a leg is out at a grain elevator 
that drops to the 60-80, something at the transformer i assume. 
This is the site i went to swap a ptp500 to a 650 last week and broke their 
manlift, this site and i have.... history, will probably be where i die, i made 
it my bitch once and had to climb up in an ice storm with two inches of ice on 
everything, 6 inch horizontal icicles, still got that up and running wearing 
khakis and a jacket.
Ever since i took its manhood, that place has treated me like its a psycho ex 
wife.

Ill rewire the cutover switch in the morning when the power company gets it 
fixed up.

I do have to have a solution for knucklehead techs though, i think i could have 
achieved the same thing with a two prong adapter. Just dont want to deal with 
osha and paperwork if i play croakamope with a tech picking up a generator

On Aug 2, 2017 8:14 PM, "George Skorup" <[email protected]> wrote:

  I see 60-80VAC at grain sites all the time when a phase is out. Pain in the 
ass. The GFI recept on the gen could just be going bad. Could also be something 
as simple as noise/surge suppression in your UPS causing it. I wouldn't worry 
about it.


  On 8/2/2017 7:12 PM, Steve Jones wrote:

    Millivolts not amps

    On Aug 2, 2017 7:08 PM, "Steve Jones" <[email protected]> wrote:

      Milliamps. But its a brownout/power outage

      On Aug 2, 2017 6:57 PM, "Jaime Solorza" <[email protected]> wrote:

        Did it read zero? If not , have that checked...we spent all morning 
with engineers, electricians and us chasing a weird diesel generator to UPS 
issue...Fluke meters galore...


        Jaime Solorza

        On Aug 2, 2017 5:51 PM, "Steve Jones" <[email protected]> wrote:

          At a grain elevator right now, brownout type issue, 60v some places 
none at others. Not our chair, not our problem, except our portable generator 
gfi trips every time the cutover switch engages.  
          We ended up just bypassing the cutover and only wiring phase and 
neutral to the generator outlet, leaving ground disconnected. I suppose we 
could have left everything intact and disconnected ground from the panel, i 
dont know

          But what we have now is phase and neutral on generator feeding the 
outlet up top, the ground is still connected to the service ground up top. We 
dont have access to a panel its connected at 

          I did measure between the ground at the panel and a known good earth 
ground. No voltage, i assume that means no hot ground.

          The concern here is if im missing something and the gfi is kicking 
because of something i dont have capacity to verify, is running this generator 
this way a risk of electrocuting somebody who touches the frame?

          Its ground is not connected in the circuit, same as if id just 
connected a 2 prong adapter