Do you want PacketFlux injectors to cost what CMMs and CTMs do? No. And neither does Forrest.

We've done several radio swaps year after year. I take a spare SyncInjector/PowerInjector/RackInjector/whatever and swap it.

Yes, it would have been cool to see the cards for the RackInjector be easily front swappable like storage on a server. Again, complexity and cost.

On 12/21/2017 2:40 PM, Darren Shea wrote:

Forrest,

That’s really interesting – am I jumping to conclusions, or does that modular design of the underlying architecture mean it would be possible to design a module which would replace the jumper options on the current RackInjector with a fully controllable, web-accessible, interface? Honestly, that’s the only reason we haven’t deployed ours – the fact we are mixing PMP450 and 450i/450m APs and ePMP 1000 and 2000 APs means that having to partially disassemble the RackInjector to change an AP is a statistically likely and pretty daunting task. Having a module to give the programmable flexibility of a LMG CTM-2M, for instance, without having to remove the unit from the rack, open up the case, and move around jumpers when switching AP types would be a big thing…

Thanks,

nDarren

*From:*Af [mailto:[email protected]] *On Behalf Of *Forrest Christian (List Account)
*Sent:* Thursday, December 21, 2017 9:57 AM
*To:* af
*Subject:* Re: [AFMUG] Remote generator start options packetflux?

I'd like to explain where we are in the grand scheme of things.    Getting the rackinjector out the door took pretty much all of our R&D engineering for the last year or so.   BUT... there's a reason for this, and it is related to the technology which is underpinning the web interface on that device.   And which is related to our fairly near-term future as far as packetflux goes...

The architecture underneath the rackinjector control system is far more layered and abstracted than it would need to be to provide just the web interface.   Every piece of data is abstracted into a generic data format inside the unit, and the system is designed in a way to greatly simplify the addition of additional features.    The overriding idea is an on-site system which is able to gather up status from the entire site and also be able to control an entire site.

To sort of give you a glimpse, in the rackinjector, there is a module for gathering up data from a NMEA GPS stream (GPS lock status, etc), a separate module for measuring the timing of the PPS pulses, a separate module for the analog digital controllers, another module to pull data from sitemonitor expansions (the expansion cards in the rackinjector are running the same underlying protocol as the sitemonitor expansion cards are today), and so on.    Each of these modules pull data from their information source and makes it available in a generic manner to the system.   For instance, the number of satellites in view is accessed in exactly the same way internally as a voltage reading.   This abstraction allows me to add additional modules to pull data quickly - all I have to do is to create a chunk of code to pull data from say a solar charge controller or pull values via SNMP from a radio.    The difficulty varies of course based on how hard it is to access the data, but it's a lot easier than writing an entire stack for each device.

Today the rackinjector is running what we call internally the "DeviceManager" code on top of this.  Generally what this is is a purpose-built web interface which is built on the underlying architecture.  The web-interface actually pulls the data it needs from the underlying system using another generic chunk of code so it is relatively easy for us to add additional fields and support for additional devices.  The "DeviceManager SNMP" module allows quick development of SNMP mibs again for specific purpose appliances.   There's a few other tricks coming as well.  Our  intent with this code base is to build a set of specific-purpose appliances to pull data largely from one device or a couple of devices and provide it in a simplified manner to the user.   For instance a Solar Charge controller monitor.  Or a RackInjector controller.  The key point here is that the DeviceManager codebase is designed largely to hide all of this from the end-user, while making it easy for us to build these products quickly.

Now, back to the main point:  This same flexible architecture permits us to also build various automated control systems on top of the same underlying architecture.  If you replace the fixed-function devicemanager interface with a programmable, scriptable, flexible interface, all sorts of things start to happen.  Including all of the items we're discussing in this thread.   We already sell all of the physical interfaces needed to get a generator controller running - you can plug a unregulated power supply into a voltage input to get a rough idea of the AC voltage, or can get the DC voltage using another voltage input.   You have contact closures in the form of another sitemonitor expansion module.   And so on.   What is missing is some sort of on-site automation, and that's where we've been heading with this entire architecture for about 2 years now.

I don't know how quickly this is going to happen.   The next 30 days I'm focused on 'finishing' the rackinjector - meaning shipping the cambium sync cards and the new 'either polarity' cards, and getting a new firmware out for it which has the "Devicemanager SNMP" code running in it.   Once that is done we can re-focus on how to prioritize the future of this architecture.

On Thu, Dec 21, 2017 at 7:40 AM, Dave <[email protected] <mailto:[email protected]>> wrote:

Forrest,
 We had a discussion about this as we now have 4 generators and I have 3 of your standby controllers taking care of
these sites without issue since we installed them.
 Would it be feasible to just remove the Transformers and just give a link for separate purchase ? My issue as with many would like to see a box with many inputs to monitor different things like AC,DC voltages, tempatures make and brake contacts. Also, the need for active outputs to turn on off things or just for a cycle with timer. A nice gui would be ok to be able to log in for manual control or configuration.

There are some very expensive things out there to do all of this but I know with a little work it can be done with out much money involved.

I have a very specific need to integrate a 26vDC generator with a site that is a 48v plant. I have everything installed and connected but I need some
automation to start and stop when needed.
The generator has a voltage sense on its output to detect if the battery bank is below 22vdc and if so it will kick on for an amount of time to restore charge. The problem with this is there is a 1000W converter between it and the 48v battery bank.

Anyone with suggestions is welcome
Dave

On 12/21/2017 03:18 AM, Forrest Christian (List Account) wrote:

    The short version:  I never sold that many, and this particular
    product came up in discussions about product liablity insurance. 
    Not that it was unsafe, just that there was some discomfort with
    the fact that I was monitoring the AC power line.    To remedy
    this I would have either had to redesign to remove the AC
    monitoring hardware, or send the whole thing through UL listing. 
     Based on the volume, I didn't really see any reason to spend a
    lot of R&D time or money doing either.

    I do expect the functionality in the generator controller will be
    able to be replicated as a side effect of planned technology to be
    incorporated in an upcoming product.

    On Wed, Dec 20, 2017 at 8:23 PM, Lewis Bergman
    <[email protected] <mailto:[email protected]>> wrote:

        Bummer. Guess there was not enough demand or to make variants?

        On Wed, Dec 20, 2017, 5:18 PM George Skorup
        <[email protected] <mailto:[email protected]>>
        wrote:

            Yeahbut Forrest doesn't make the generator control board
            anymore.

            On 12/20/2017 5:01 PM, Lewis Bergman wrote:

                I think packetflux is likely the easiest with the most
                to offer our of the box. I know if one other out of
                the box solution that cost about 3 times as much.
                First can not only start it but he can use his shunt
                to make sure it is actually started and producing current.

                If you want to do it yourself you could work some
                coding and such but it doesn't sound like that is what
                you want to do. Arduino, raspberry pi, etc. Could do
                this but you have to build it all yourself. Not really
                fast but fun if you like that kind of thing.

                You would need some electronics knowledge if you don't
                want to spend a few days googling. I guess you still
                have to know enough to make Google work.

                Again, see Forest for his genset setup. I know a lot
                of people in this list use it.

                On Wed, Dec 20, 2017, 4:39 PM Eric Kuhnke
                <[email protected] <mailto:[email protected]>>
                wrote:

                    assuming you have a generator that does auto-choke
                    and is wired for electrical remote start, like the
                    small generac units sold for RV use and similar...
                    where all you need to do is turn on a relay for
                    4-5 seconds to crank a starter, then turn off the
                    relay again.

                    one of these: http://tinycontrol.pl/en/lan-controller/

                    and one of these:
                    http://tinycontrol.pl/en/relays-board-10a-v3/

                    or a thing like this:
                    
http://denkovi.com/ethernet-relay-card-5-channels-snmp-http-xml-real-time-clock-din-box

                    there are quite a few different DIN mount
                    relay-controllers with basic http interfaces to
                    turn on and off things. Some support things like
                    receiving an snmp trap to trigger a relay for
                    automated scripting.

                    On Wed, Dec 20, 2017 at 2:30 PM, Brandon Yuchasz
                    <[email protected]
                    <mailto:[email protected]>> wrote:

                    We are looking at adding a remote start to a
                    generator at an off grid site we have and I am
                    gathering information  on options at this point.

                    Right now we are all Solar at the site.  It’s a
                    new site and if / when we draw down batteries
                    beyond where we are comfortable we turn go to the
                    site turn off the PV and start a generator
                    manually and run a 48v battery charger on the
                    bank. It’s a fairly low tech solution right now.
                    We log in turn off the PV array and a guy goes out
                    and pulls the rope on the generator and batteries
                    start to charge. He then leaves and in three hours
                    generator runs out of fuel and charging stops. Log
                    back in turn the PV back on and that’s the end of
                    the process.

                    We are considering a few different options at the
                    site and I don’t want to complicate this to much
                    by offering to much information to start. Ill go
                    into more details later but for now I am looking
                    for a way to start a (different) propane generator
                    remotely during the dark months. Most likely once
                    a week in December and January.

                    So assuming electric start is an options on the
                    generator. What options do I have for throwing
                    that “switch” from the office. I am positive I am
                    not the first one of us to want to do this.

                    Thoughts everyone? I want to KISS so when I am not
                    around others can do this with minimal training.

                    Thanks,

                    Brandon



--
    *Forrest Christian*/CEO, PacketFlux Technologies, Inc./

    Tel: 406-449-3345 | Address: 3577 Countryside Road, Helena, MT
    59602
    
<https://maps.google.com/?q=3577+Countryside+Road,+Helena,+MT+59602&entry=gmail&source=g>

    [email protected] <mailto:[email protected]> |
    http://www.packetflux.com <http://www.packetflux.com/>

    <http://www.linkedin.com/in/fwchristian>
    <http://facebook.com/packetflux> <http://twitter.com/@packetflux>

--



--

*Forrest Christian*/CEO, PacketFlux Technologies, Inc./

Tel: 406-449-3345 | Address: 3577 Countryside Road, Helena, MT 59602

[email protected] <mailto:[email protected]> | http://www.packetflux.com <http://www.packetflux.com/>

<http://www.linkedin.com/in/fwchristian> <http://facebook.com/packetflux> <http://twitter.com/@packetflux>


Reply via email to