On Mon, 1 Dec 2025 at 14:34, Jon Perryman <[email protected]> wrote:

> On Mon, 1 Dec 2025 11:10:24 -0500, Steve Smith <[email protected]> wrote:
>
> >I do think that this premature optimization is a bit much for
> >initialization code.  Making it simple is more important.
>
> What is it that makes these 256 bytes very time sensitive for the op?
> Everyone has ignored that this is for an automation product. Automation
> products can be greatly affected by very small time windows.
>
> This probably isn't about optimization. Instead, it's more likely about
> avoiding a deadlock or synchronization situation. More likely than
> initialization, this is probably about resetting the counters.
>
> Solution 1: Instead of zeroing counters, make a copy of the counters and
> subtract the previous counters from the copy to give the delta. This
> solution requires the counters be binary.
>

Not obvious to me why this approach requires binary counters, or why you
say (1) and (2) both require binary.
.

> Solution 2: Use binary numbers instead of packed and XC the 256 bytes.
> You'll still need a copy of the counters for your calcs and counters can be
> incorrect because you can't serialize.
>

Not so. On any modern machine (post 2010 or so), which will have
the Interlocked-Access Facility 1 installed, a handful of instructions
provide interlocked updates. Notably Add Immediate (ASI and AGSI) and Load
and Add (LAA, LAAG).

Solution 3: Replace the pointer to the counters with a pointer to the new
> counters. Wait 30 seconds before using the old counters in case something
> is inflight. Not my first choice of solutions because a storage overlay can
> occur if something takes longer than 30 seconds.
>

No - just no. Unless you're prepared to use Compare and Swap and friends,
and fully understand how to use them.

Tony H.