On Fri, 22 Jan 2021, John Edwards wrote:

Underground copper is probably more vulnerable than aerial to lightning. Lightning strikes the ground, not the copper, but a voltage gets induced in the copper due to the nearby electromagnetic charge - something that doesn't happen in air because it's a fairly good insulator.

My experience has shown a different path to lightning damage.

When lightning strikes the ground, or a grounded object, that current dissipates through the soil, which has a typical resistance of around 500 ohms per metre. If you have tens of thousands of amps flowing, then ohms law tells us we have potentially huge potential differences over even fairly short distances.

The copper cable has a very low resistance (by comparison).
If that cable happens to be radial (or oblique) to the current path from the point of entry, the potential difference from one end of the cable to the other will be hundreds to many thousands of volts.

Even the insulation of the cable may not be enough to save it, and any components connected to it which happen to be physically close to the ground will certainly break down.

This can happen at distances far further away than magnetic induction alone would explain. It also explains (to me anyway) why I've seen burried cables damaged part way along their length (where the greatest potential difference has been).

Just my take on it.
R.
_______________________________________________
AusNOG mailing list
[email protected]
http://lists.ausnog.net/mailman/listinfo/ausnog

Reply via email to