Something that I have to keep reminding beancounters with A/B planning is don’t 
go above 40% load on either side.

 

Its very difficult to convince a CFO who’s entire life is spent with a 
spreadsheet open in front of him is that N+1 means typically Double, and that 
Kw != Kva.

 

 

From: AusNOG <[email protected]> On Behalf Of Matt Perkins
Sent: Tuesday, March 14, 2023 9:18 AM
To: Christopher Hawker <[email protected]>; Nathan Brookfield 
<[email protected]>; [email protected]
Subject: Re: [AusNOG] Vocus Datacentre outage.

 

The questions left to be answered for Vocus is why did it take 12 hours to 
restore one rail. Where was the static bypass and failing that where was the 
maintenance bypass.  Im guessing that's what it's on maintenance bypass now and 
the slow action may have something to do with the public holiday in Vic..  

 

I shouldn't speculate. But it is fun. 

 

 Something seriously let go in that UPS. If i had to put my electrical 
engineers hat on I would say their load capacitor maintenance was not done and 
let go. Or someone was working upstream and broke the natural/earth bond. But 
there's a lot of parts in a system like that , most modern DC UPS setups are 
fairly robust.  I once had 3 strings of batteries catch fire and melt down and 
the UPS didn't miss a beat other then spewing a lot of alarms. We moved strings 
around on the fly and nobody even noticed.   

 

The other things that seems odd is why did an A failure trip B.  Sounds like a 
single supply is at surge/break capacity. Also a worry.  

 

But in the end we all have redundancy around 530 Collins right ? Right ? 

 

Matt

 

 

On 14/3/2023 11:50 am, Christopher Hawker wrote:

SY1 apparently experienced a full power outage back in July 2009, according to 
AusNOG Archives. Some reported full outages, some partial. Was not a DC fault 
though, looks like a much larger grid issue where a fault at the Bayswater 
Power Station in the Hunter Valley (which affected generators in QLD and VIC) 
caused about 1000MW to be dropped from the grid, resulting in rolling blackouts 
across QLD, NSW, TAS, SA and VIC.

 

https://lists.ausnog.net/pipermail/ausnog/2009-July/003222.html

 

CH.

  _____  

From: AusNOG  <mailto:[email protected]> 
<[email protected]> on behalf of Nathan Brookfield  
<mailto:[email protected]> <[email protected]>
Sent: Tuesday, March 14, 2023 11:40 AM
To: Matt Perkins  <mailto:[email protected]> <[email protected]>; 
[email protected] <mailto:[email protected]>   
<mailto:[email protected]> <[email protected]>
Subject: Re: [AusNOG] Vocus Datacentre outage. 

 

Have 100% had A and B fail separately at SY1 but never both, thankfully!!!

 

Could have been part of the facility though so don’t quote me.

 

UK on the other hand, fail!

 

From: Matt Perkins  <mailto:[email protected]> <[email protected]> 
Sent: Tuesday, 14 March 2023 11:30 AM
To: Nathan Brookfield  <mailto:[email protected]> 
<[email protected]>; [email protected] 
<mailto:[email protected]> 
Subject: Re: [AusNOG] Vocus Datacentre outage.

 

SY1 had A or B fail a few years back if my memory serves me correctly.  But I 
was referring  London and Manchester which both had total outages in recent 
years. 

Matt.

 

On 14/3/2023 11:26 am, Nathan Brookfield wrote:

I’ve never had an A+B power rail failure at Equinix in 18 years I’ve been in 
there facilities, TOUCH WOOD!!!

 

Nathan Brookfield | VK2NAB
General Manager

p: 1300 592 330 | m: 0412 266 008
e: [email protected] <mailto:[email protected]>  
| w: iperium.com.au

Suite 4.02, 189 Kent Street Sydney NSW 2000


Your Telco Team

DISCLAIMER: This document is intended solely for the named addressee. This 
electronic communication, which includes any files or attachments thereto, 
contains proprietary or confidential information and may be privileged and 
otherwise protected under copyright or other applicable intellectual property 
laws. The use, disclosure, copying or distribution of any of the information 
contained in this document, by any person other than the addressee, is strictly 
prohibited. If you received this document in error, please contact the sender 
immediately and delete all the material from any computer. Confidentiality and 
legal privilege are not waived or lost by reason of mistaken delivery to you. 
Any views or opinions presented are solely those of the author and do not 
necessarily represent those of Iperium. 

WARNING: Computer viruses can be transmitted via email. The recipient should 
check this email and any attachments for the presence of viruses. Iperium 
accepts no liability for any damage caused by any virus transmitted by this 
email.

From: AusNOG  <mailto:[email protected]> 
<[email protected]> On Behalf Of Matt Perkins
Sent: Tuesday, 14 March 2023 11:18 AM
To: [email protected] <mailto:[email protected]> 
Subject: Re: [AusNOG] Vocus Datacentre outage.

 

Yea because Eqinix has never had a power outage. :) 

I think it's a little premature to judge at the moment. Doesn't sound good 
based on the current info but we have all had bad days im sure.  

Matt

 

On 14/3/2023 11:06 am, Bradley Amm wrote:

Friends like let friends put gear in a Vocus dtacenter. Only NextDC or Equinix 
:) 

Sent from my iPhone





On 14 Mar 2023, at 7:08 am, DaZZa  <mailto:[email protected]> 
<[email protected]> wrote:

 

Doesn't say a whole lot about Vocus' data center design methodology, nor their 
periodic contingency testing.

 

They're apparently replacing the entire UPS on Friday - guess we can all expect 
more outages then when they stuff that up.

 

D

 

On Mon, 13 Mar 2023 at 18:30, Chad Kelly <[email protected] 
<mailto:[email protected]> > wrote:

Thought I would create a new thread on this, as the issue wasn’t related to 
AussieBB. 

It is looking like this Melbourne outage is similar to the Sydney outage back 
in 2018, in that it appears to have been yet again caused by an issue with 
their UPS systems yet again.

I’ll leave this hear 
https://www.arnnet.com.au/article/633314/servers-australia-uproots-services-after-vocus-data-centre-outage/
 and this article on today’s outage as well. 

https://www.itnews.com.au/news/vocus-melbourne-data-centre-hit-by-power-outage-591987

 

Regards Chad. 

 

 

 

Chad Kelly 

Manager 

CPK Web Services 

Phone 03 52730246

Web https://www.cpkws.com.au

<image001.jpg>

 

_______________________________________________
AusNOG mailing list
[email protected] <mailto:[email protected]> 
https://lists.ausnog.net/mailman/listinfo/ausnog



-- 

veg·e·tar·i·an:
Ancient tribal slang for the village idiot who can't hunt, fish or ride

_______________________________________________
AusNOG mailing list
[email protected] <mailto:[email protected]> 
https://lists.ausnog.net/mailman/listinfo/ausnog





_______________________________________________
AusNOG mailing list
[email protected] <mailto:[email protected]> 
https://lists.ausnog.net/mailman/listinfo/ausnog

-- 
** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL 
 
/* Matt Perkins
        Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
        Office 1300 133 299     [email protected] 
<mailto:[email protected]> 
        ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
 
*/

-- 
** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL 
 
/* Matt Perkins
        Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
        Office 1300 133 299     [email protected] 
<mailto:[email protected]> 
        ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
 
*/

-- 
** DO NOT SEND PRIVATE OR CONFIDENTIAL MATERIAL VIA EMAIL 
 
/* Matt Perkins
        Direct 02 8916 8101     Spectrum Networks Ptd. Ltd.
        Office 1300 133 299     [email protected] 
<mailto:[email protected]> 
        ABN 66 090 112 913      Level 6, 350 George Street Sydney 2000
 
*/
_______________________________________________
AusNOG mailing list
[email protected]
https://lists.ausnog.net/mailman/listinfo/ausnog

Reply via email to