I won't add to the recommendations that avoid retasking a PDU
that isn't rated for how you're going to use it. I agree that it's a
bad idea.
As for vendors, you might also want to check out servertech.com
in addition to APC. I've been quite happy with their product line.
-R. Gary
On 4/2/14 12:42 PM, Jeff Wasilko wrote:
On Wed, Apr 02, 2014 at 12:30:35PM -0400, Scott Danek wrote:
Hi all,
We're looking into increasing our power in our colocation from 120V 20 amp
to 120V 30 amp so that we can add more equipment. When looking for PDU's
it seems that a PDU that will take a 120V input and output 30 amps is
uncommon. Most 30 amp PDU's we've seen seem to take a 200V+ input. If we
got a PDU that lists a 200V or 208V input and output, and plugged it into
a 120V circuit, what would be the outcome? Would that be ill-advised?
Thanks!
APC makes them at least:
http://www.apc.com/resource/include/techspec_index.cfm?base_sku=AP7802
Better thing might be to upgrade to 20A 208V.
30A 120V gets you 3600 watts
20A 208V gets you 4160 watts.
-j
_______________________________________________
bblisa mailing list
[email protected]
http://www.bblisa.org/mailman/listinfo/bblisa
_______________________________________________
bblisa mailing list
[email protected]
http://www.bblisa.org/mailman/listinfo/bblisa