David Kewley wrote:
David,
The reboots were due to a City of Pasadena power glitch at 9:17 that
morning. :) It was raining, and a 34kV city feeder line that runs between
the generating plant at the entrance of the 110 and a substation at Del Mar
& Los Robles faulted. The responsible breaker took 13 cycles to break,
during which time the single-phase voltage seen at Caltech dropped to about
75V.
induce massive 12Hz oscillations on the room's power lines.
As for the time glitch, that is probably induced by the fact that Daylight
Savings Time changes only take place on the "system" clock, and in a
standard Red Hat system those changes only get synced to the hardware clock
upon a clean shutdown. So if your machine crashes after a DST change, then
upon bootup syslogd gets its time from the hardware clock, which is wrong.
The system clock is only corrected later in the bootup sequence, when ntpd
starts. The best solution is probably to set the hardware clock to UCT
rather than local time. UCT doesn't undergo step changes like most
timezones in the U.S. do, so the compensation for DST happens dynamically
in software, rather than requiring a hardware clock change.
Why don't you use a line conditioner ? It's much cheaper than a similar
powered
UPS ($1000 for 10kW), many UPS dont guarantee voltage and waveform excepted
during clean power cuts, anyway.
A line conditioner is very handy in time of brownouts like during August
thunderstorms.
We have a Salicru one on our cluster and have a much better MTBF on our
compute nodes in comparison
with the ones of a computing room nearby.
Besides, I was confronted with the same problem about daylight saving time.
Just added a
clock -w
after the NTP synchronization in cron.daily so that the time would be
corrected automatically
on the hardware clock. (which is automatic on Windows btw).
_______________________________________________