This link has a lot of good information and might answer your question:

http://www.mediarecovery.com/hot_topics/cooling_problems.php

as long as you're alert to the fact that it's an APC marketing document.
for instance:

        It is unlikely that a traditional data center, with computer room air
        conditioning (CRAC) units supplying airflow through a raised-floor 
plenum,
        will be able to deliver a cooling capacity of more than 3 kW to any 
rack,
        regardless of quantity and capacity of CRAC units and floor depth.

by "traditional", perhaps the author means "designed for < 3kW/rack",
but if so, the sentence implodes...

a traditional data center with a simple ~14" raised-floor and free-air return
can indeed cool >10 KW racks just fine.  the first few suggestions (maintain
your chillers, install blanking panels, tidy up your cables) are fine, and I
hope fairly obvious.  items 5-8 are all somewhat arguable.  interestingly, I
was worried about figure 10 (suction in tiles too near the chiller), but am
surprised that even as close as 6 feet from a high-velocity outflow, tile
flow is adequate and upward.  items 9,10 are just APC sales pitches.