hi all,     
forgive me as a new kid on the block for telling some of you how to suck eggs,  
and what i am about to point out may not apply in north america or canada, but 
it certainly applys here in the uk where our supply line is between 230 and 240 
volts. so in case someone is on the list that this may effect, i feel i should 
point out a potential hazard of using plastic pipe. 
living in northern ireland, we have used something similar to pex for a few 
years now. however there is one big disadvantage in using plastic piping of any 
kind, especially in europe.

i am not sure what the situation is in north america with the electrical 
supply, do you use an electrical earth connection? and if so how do you get 
this connection?
i know most of your supply lines are around 110 volts, and in some cases for 
cookers or stoves it may be in the region of 240 volts, but here in this part 
of the uk all our appliences   that have a metal frame must  be connected to an 
electrical safety earth. 
for those who dont know what this is, it is a common wire that connects to the 
frame of evrything metal that has an electrical supply throughout the house. 
this includes dish washers, washing machines, stoves, water heaters and 
centeral heating, centeral air etc.   this is to allow a faulty applience to be 
able to blow a fuze or trip before it kills someone. 
 now if the wireing has been done properly, there should be no problem, but the 
potential for electrical shock is high if someone who doesnt know what they are 
doing comes along and does a bit of handy work either to the plumbing or the 
electrical instillation.
heres why.

because all appliences and instilations with  metal caseings need an electrical 
safety earth connection attached to them, here in the u.k. it is regulation 
that all metal pipes throughout      the building is bonded together with at 
least a 6 mm copper wire.  as i said earlier, if this is done properly and left 
alone , there should never be any problem. this is because on modern 
instillations the earth is taken from the supply cable at the meter board, and 
is common with the neutral return wire. however on  old instillations, 
especially in the country areas where overhead supply cables are a common 
sight, more often than not the earth return path is made by either an earth 
spike, which in some instances is just connected to the water pipe at the point 
where it entered the house, or dread the thought, even by just relying on the 
old water main itself, which in days gone by was either copper or lead.
this worked well for many years, that was untill someone invented plastic pipe. 
because by breaking the continuity of the earth by replaceing a piece of 
damaged lead or copper pipe with plastic,  they take away the safety aspect of 
having an earth connection which goes  to earth, and subsiquently back to the 
municipal supply.  in lots of cases this was never noticed untill someone 
developed a fault on the system. lets say you got a falty water heater that 
decided to short to the copper cylinder that it was enclosed in. if the earth 
was working properly, this would normally blow the fuse or trip switch. however 
because it now cant find a path back to earth via the old copper or lead pipe, 
it just sits there and looks for the path of least resistance to earth. 
hopefully this is not you! the applience may still work, however because the 
pipework  in the house is acting as an electrical conductor,  evrything else in 
the building on the household side of the plastic join will become live and 
have the potential of causing serious shock or death.  this can happen if you 
dont know there is a problem and you grab onto something metal, such as your 
cooker or sink.
or if you disconnect  any of the metal pipework at your hot water cylindar that 
is not cross bonded to all the other pipes that are close by. 
this is only a couple of sinarios, there are of corse many other instances on 
how electrical shock  can happen if there is not the proper care taken.
there is of corse an easy resolution to this potential problem, and that is 
should you ever have the need to replace a piece of metal   pipe  with plastic, 
you should also run a piece of 6 mm earth wireing along side it, and clamp it 
to the metal pipe on each side of the join. this ensures that the earth 
protection is not broken. 
however if you are not sure where you get your earth supply from, just in case 
there is a fault that may not be evident, if possible you should consider 
switching off your electric supply when replaceing a section of existing metal 
pipework with plastic. 
on no account should you grab on to both ends of the old pipework with both 
hands once it has been cut. 
  as i said earlier, forgive me if this does not apply to you, but it certainly 
will apply in some countrys throughout the world.
it is known for a voltage as low as  50 volts to cause serious damage to anyone 
who is not in good health, should they get it going to earth across their 
chest. 
and if you must work on wireing that is live,  do it with the knowlege that 
electricity is silent but deadly, so always have someone else around you when 
you are doing this.. 

heres a safety quote from a sparks point of view.

its the volts that jolt, its the mils that kill.
be safe, stay safe, and ask questions before you start working with plumbing or 
electric.
i can answer any questions on this subject  should you wish to ask them. 
best wishes to all, 
Dave & Sally. 
buy and sell your surplus free, join the new mailing group by sending a blank 
email to. [EMAIL PROTECTED]

or find more details here. 
http://www.secretsthatwekeep.com/thebargainstore/invite.htm


----- Original Message ----- 
From: Boyce, Ray 
To: [email protected] 
Sent: Wednesday, September 12, 2007 11:09 PM
Subject: [BlindHandyMan] Easier Plumbing with PEX


Next time you need to replace pipes in your home, consider an
alternative to rigid piping that comes in rolls, can be cut easily to
any desired length,
and requires no soldering and very few joint fittings. Generically
called PEX-AL-PEX, this flexible plastic piping is so easy to install
that you can handle
most projects quickly on your own.

Although PEX-AL-PEX is relatively new to North America, it's approved in
major plumbing codes, and professional plumbers are increasingly
choosing PEX-AL-PEX
because of its successful 30-year track record in Europe. It's a little
more expensive than rigid copper piping - but the advantages outweigh
the extra
cost. Plus, you can save money by doing the job yourself. You can buy it
at major hardware stores, where it's usually sold as water supply piping
and infloor
radiant-heat lines. When you buy PEX at the hardware store, make sure
the tubing is stamped with "NSF-61" or "NSF pw" (for potable water),
which distinguishes
it from the PEX that is used only for infloor radiant heating
applications.

PEX-AL-PEX is named for its sandwich-layered construction that uses
cross-linked polyethylene plastic as the outside layer (PEX), aluminum
as the middle
layer (AL) and another layer of cross-linked poly on the inside. To keep
it simple in this article, I'll refer to PEX-AL-PEX as just PEX, though
that name
also is used for plastic-only water supply lines.

PEX is worth considering for your next plumbing project for three
reasons:

Flexibility. PEX can be hand-bent in any direction and will remain in a
fixed position. This allows you to work it around and through existing
floor joists,
walls and frame members. PEX bends tightly up to a 3-inch radius without
forming kinks, which significantly reduces the need for most elbow
joints.
Worksaver

Easy joint assembly. PEX joints usually are made with either threaded
compression fittings
or
crimp-on connection rings
(both described below). These joints are fast and easy to complete, and
you don't have to torch and solder them, except when you connect new PEX
lines to
existing copper supply pipes. But even connecting copper pipes to PEX is
a job that most people can do themselves - all it takes is some basic
knowledge
of plumbing skills and PEX joints (see "
Connecting to Copper
").

Resistance to frost cracking. PEX piping is better than rigid piping at
resisting the outward pressure of freezing water. Manufacturers
typically test and
warrant their aluminum-core PEX lines to withstand five freeze/thaw
cycles before cracking may occur. PEX may withstand even more than that,
but it isn't
completely immune to frost cracking.

Octopus Manifold & Fittings

To get the most value out of your PEX lines, you need to plan
differently for a PEX installation. Instead of following a roadlike
network of large pipes
that would normally feed smaller ones in straight-line fashion, water
flows from the main PEX line to a central location called a
manifold,
which in turn feeds smaller PEX lines (similar to the arms of an
octopus) that supply fixtures directly.

This configuration delivers consistent pressure to all PEX-connected
fixtures, because it creates a hub where water is equally directed to
various points
in the house. The line supplying your manifold should be three-fourths
inch in diameter, with half-inch-diameter branch lines sprouting off
from the manifold.

To connect separate pieces of PEX to valves, manifolds and joints, you
have a choice between compression fittings and crimp-on rings.
Compression fittings
connect with threaded parts you tighten together. For small jobs
involving less than 20 joints, compression fittings are the most
cost-effective option
for PEX. To attach a compression fitting, just slip a nut onto the PEX,
push the cut end of PEX line over the O-ring on the end of the fitting
and tighten
the nut with a couple of wrenches (see "
9 Essential Wrenches and Pliers
").

Compression fittings are faster, easier and safer to install than any
solder joint, but the drawback is they are relatively expensive. For
smaller jobs,
you can justifiably spend $5 or more on a threaded elbow, a connector or
a T-shaped compression fitting. But for bigger jobs that require many
fittings,
the cost will add up.

Professional plumbers almost always prefer
crimp-on connection rings
because they're less expensive, and they install faster and easier than
wrench-tightened compression fittings - but there's a catch.
Crimping tools
can cost several hundred dollars each, and you'll need one tool for
half-inch joints and yet another for three-fourth-inch joints. The price
of these tools
is justifiable only if you are plumbing more than one building. Crimping
tools are durable, which makes them good candidates for a shared
purchase among
several neighbors. Keep them oiled and indoors, and they'll last
forever.

The crimping rings themselves are simple, inexpensive metal bands that
work great. Just slip one onto the PEX, assemble the joint, slide the
ring over the
joint, open the jaws of your crimping tool over the ring, then squeeze
the jaws shut. The force of the crimping tool makes the diameter of the
ring slightly
smaller, resulting in a tight and permanent joint. But before you use
the tool, make sure you've got the joint positioned where you want it.
The only way
you can pull the joint apart later is by cutting off the crimped ring
with a hacksaw and prying it off the PEX line.

Before you buy PEX and plumbing supplies, create a schematic drawing of
your proposed layout. Mark the location and type of any fittings you
will need,
and note any major obstacles caused by framing details or inconvenient
routes. By doing this, you can make a list of all the supplies and tools
you will
need before making a trip to the hardware store. As you plan your
layout, remember that the flexibility of PEX offers potential for
designs not possible
with rigid piping. For instance, you can run PEX lines through holes
drilled in floor joists, keeping your pipes tucked up inside the floor
frame, where
they will be out of the way.

Installing PEX

After you've planned your layout, bending and positioning your PEX is
easy. But before the job is done, you'll also need to cut, ream and
install joints
in PEX; drill holes in wood and drywall; and connect hoses to fixtures.

Boring holes. To drill holes through walls, joists or drywall, use a
1-inch-diameter self-feeding auger for half-inch water lines, and a
11/4-inch auger
for three-fourths-inch lines. Ample clearance reduces installation
friction when you pull the PEX lines through the holes. Putting in PEX
lines this way
is much like pulling heavy electrical cable, so recruit someone to help
you. Have your helper unroll 10 or 12 feet of PEX from the coil, then
pull it into
place before unrolling more.

When installing PEX in floor joists, the only difficulty you'll likely
encounter is boring all those holes in tight quarters. To drill these
holes, your
best option is a cordless right-angle drill with a short self-feeding
auger bit. To align your cuts, follow the joint lines of the plywood
subfloor, or
snap a chalk line along the bottom edges of the joists. The more uniform
the hole location from joist to joist, the easier it will be to pull the
PEX lines
into place.

Cutting. You can cut PEX with specially designed,
inexpensive shears
that have a single metal blade. The trick to cutting PEX with this tool
is making a two-step slice: With the first stroke, cut most of the way
through the
tube, rotate the shears a quarter-turn and then finish with another
squeeze. Whatever you do, don't struggle using a hacksaw or copper pipe
cutter - neither
cuts PEX very well.

Reaming. The pressure required to cut PEX doesn't flatten the pipe
completely, but it does create an oval profile that you need to correct.
That's why the
next step in completing a joint involves widening the opening of the PEX
line with a simple tool. The
reaming tool
does two things: It imparts a perfectly round shape to the inside of the
pipe, while also chamfering (beveling) the inside edges of the opening
to prevent
damage to the O-rings that seal the fittings after assembly. Cutting and
reaming each joint takes just seconds, but be sure you ream carefully
and evenly.
The inside edge of the PEX line end must be a smooth, beveled surface.
If you leave behind a sharp edge or a stray piece of plastic, the
all-important
O-rings in the joint can become damaged and cause a leak.

Installing valves. When you install any new plumbing, you should test
the system for leaks before hiding the pipes behind drywall or paneling.
That's why
it's a good idea as you work to install
shut-off valves
at the end of each run of PEX. Later, you'll need the valves to shut off
the water during fixture maintenance, but the valves also serve a useful
and immediate
purpose. You can turn on the main water supply valve and then bleed off
air using each individual shut-off valve. This lets you look for water
leaks that
probably wouldn't be visible if small amounts of air were leaking out of
the pipe. Even if you forget to tighten or crimp a joint connection, the
O-rings
alone will often prevent leakage in PEX installations, at least
temporarily. You should double-check that each joint is tight, even if
the connection appears
leak-free after you bleed off the trapped air.

If you're plumbing a seasonal home and you plan to drain the system each
fall, then install your PEX water lines on a slight slope toward a drain
valve
in a convenient location that will allow the water to run out. This way,
you can easily drain water when you expect freezing conditions. Don't
guesstimate
the slope, either. Measure, snap a chalk line and then bore holes to
make an evenly tilted line through building frame members. Dips in the
slope will
result in PEX with left-behind pockets of water, which could result in
cracking after numerous winter freezes.

Connecting to fixtures. Eventually, all your lines of PEX will connect
to fixtures, faucets and water bowls that supply your house, barn and
outbuildings.
These fixtures are not made to accept PEX lines directly, so you'll need
to add transitions. The best way is to install a shut-off valve with a
threaded
end that's designed to accept a flexible, reinforced supply line. Supply
lines range in length from 8 to 24 inches and are made from neoprene,
reinforced
with a mesh of braided stainless steel that's wrapped around the outside
to increase the resistance to water pressure inside the line. Place the
ends of
each PEX line 8 to 12 inches away from where you think the connection
point for your fixtures should be located. The braided flex line will
get you the
rest of the way without hassles.

The do-it-yourself advantages of PEX piping are a clear indication that
wisely chosen newer building materials can be a big help for people with
a heart
for self-reliance. All that's required is a bit of knowledge about the
materials and methods of building, faith in ourselves and initiative to
get the
job done.

Connecting to Copper

You will need a special fitting when connecting PEX lines to existing
copper supply pipes. One end of this fitting is soldered into either
half- or three-fourths-inch
copper, and the other end includes O-rings and a profile that accepts a
PEX line. (
See photo.)

The O-rings must be removed before you solder the fitting. To remove the
soft O-rings, squeeze them with two fingers to create a bulge in the
rubber that
you can grab with your other hand. (The O-rings can become damaged if
you try to grip them with pliers or a screwdriver.) After the O-rings
have been removed,
clean the copper joint with sandpaper, brush on a coat of soldering
flux, heat it up and then apply solder. Only when the metal is
completely cool can
you safely reinstall the O-rings and complete the joint.

**********************************************************************
This message and its attachments may contain legally
privileged or confidential information. If you are not the
intended recipient, you must not disclose or use the
information contained in it. If you have received this e-mail
in error, please notify the sender immediately by return
e-mail and delete the e-mail.

Any content of this message and its attachments which
does not relate to the official business of Eraring Energy
must be taken not to have been sent or endorsed by
Eraring Energy. No warranty is made that the e-mail or
attachment(s) are free from computer virus or other defect.
**********************************************************************



[Non-text portions of this message have been removed]



To listen to the show archives go to link
 http://acbradio.org/handyman.html
or
ftp://ftp.acbradio.org/acbradio-archives/handyman/

The Pod Cast address for the Blind Handy Man Show is.
http://www.acbradio.org/news/xml/podcast.php?pgm=saturday

Visit The Blind Handy Man Files Page To Review Contributions From Various List 
Members At The Following address:
http://www.jaws-users.com/handyman/

Visit the archives page at the following address
http://www.mail-archive.com/[email protected]/  

If you would like to join the Blind Computing list, then visit the following 
address for more information:
http://jaws-users.com/mailman/listinfo/blind-computing_jaws-users.com

For a complete list of email commands pertaining to the Blind Handy Man list 
just send a blank message to:
[EMAIL PROTECTED] 
Yahoo! Groups Links




[Non-text portions of this message have been removed]

Reply via email to