Boxes come in two basic types Metal and Plastic.
For general residential construction the choice is left up to the contractor 
and if the box is not exposed then it will most often be a plastic box. 
Exposed
boxes like the ones found in unfinished basements and outside the home are 
made of metal this is to reduce the risk of breaking the box and then having
exposed wires.

Installing Boxes
Whether the box will be for a light switch or an electrical outlet there are 
a few rules to follow when installing the box.
The first is off the ground height. The National Electric and Building Codes 
will set the minimum and maximum height from the ground that all boxes must
be set. If there are reasons such as accessibility for handicapped these 
codes can be adjusted.

During inspection all electrical boxes, wires and connections must be 
visible or accessible to the inspector.

New Construction boxes are nailed to the stud prior to installing the 
drywall.
Most boxes will have a gauge or clip on them so when you rest it against the 
stud the front of the box will protrude far enough that drywall can be 
applied
and the box will be flush with the outside surface.

Post Construction or Retrofit boxes may come with clips that allow them to 
be attached within the wall cavity. The use of these boxes is really a last 
resort
and the only reason is to allow fast installs without damage to the drywall. 
If you are planning to use such a box you should really install the box 
against
a stud and nail the box from the inside to the stud. It is not that much 
extra work and will make sure the box is secured properly and not able to be 
ripped
from the wall.

Exposed Boxes
Often in garages or basements you may find a box on a concrete or bare stud 
wall that is not protected. In this case you must use a Metal Box that is 
designed
to accept Conduit. Conduit pipe will be used to protect the wire that is run 
to the box. When you install conduit and metal boxes you will need to use
a conduit tube bender. An offset is necessary at the point of the box to 
make the attachment.

Outdoor Boxes
Boxes that are exposed to the outside must be weather tight and should be 
metal. There are PVC plastic boxes that are available but the danger with 
using
a plastic box is impact destruction. Outside switches and outlets can be 
covered with a flip up cover or some switches are weather tight and exposed. 
When
choosing any product for outdoor service you should follow recommendations 
of both electrical code and the manufacturer. A box that holds water even 
days
after a rain will be a danger to anyone near or using it.

electrical gang boxGang Boxes
Some boxes will come pre made to accept more then one switch or outlet. The 
most common is 2 or three but 4 or more can be made. Plastic boxes are not 
the
best choice for gang boxes unless they are pre made. Special attention must 
be made to ground the box and not just the switches when you use a metal 
gang
box. If you find that you are installing more then 4 switches or outlets in 
one location you may want to rethink your circuit plans. Locating the 
switches
within a sub circuit breaker box or separating the switches by 1 or more 
wall void spaces will reduce confusion.

Junction Boxes
There are situations where a connection between 2 sub circuits must be made 
this can happen during initial construction or when you are retrofitting a 
building.
Where you can not make connections within an outlet or switch box you must 
use a junction box to protect your splice. For instance you are running more
outlets in your garage to install a garage door opener or outlets in 
different areas. The wire to the garage is located in the attic craw space 
however
gaining access to the installed boxes is not possible. Where you cut the 
wire to make a splice you will install a metal box and connect it to a stud. 
Make
all connections with wire nuts and install a cover plate to protect the 
junction.

When installing special appliances there are other types of boxes that are 
only to be used for that situation. Follow manufacturers instructions for 
any
such install. Ceiling Fan boxes are both the support and the connection 
point for your fan. They come in 2 types New and Retrofit Construction. Be 
very
careful to follow instructions closely and do not use a standard wall box 
for a ceiling fan.

Some items like furnaces and water heaters should not make use of a box and 
should be hardwired. This means a direct wire from the circuit breaker into
the appliance / furnace.

Electrical wiring can be a danger if it is not performed correctly. If you 
have any doubts in your ability and if you have not attempted such a project
before in the guidance of a professional then you should contract with a 
licensed electrician. 