"I have noticed that the light that shows when the pid is calling
   for heat is not steady, it's on and off. I'm pretty sure that helps
   with temp overshoot and under temp conditions."

Yup, that's the idea. The PID controller measures not just the current temperature, but monitors it over time and does some calculus to determine the optimal power level needed to reach the set point or maintain it if it's already there. The output of the PID calculation is not just on or off like a thermostat but a numeric power percentage. It then takes that number and "pulse code modulates" it--i.e. quickly turns the element on and off--to achieve the desired power level.


On 1/21/2016 11:51 AM, herman dickens wrote:
Fwiw I just completed a similar operation on my brewtus II today. I upgraded to a pid. The cost was 235 for all the parts. I had to remove the old thermowell and thermocouple and install the pid sensor. I removed the old display and the PID display fit perfectly in the old opening. I had to drill 2 holes in the base to mount the new relay. I also had to extend 2 wires that were not long enough. The kit I used had all of the screws, connectors, heat shrink tubing, and parts necessary to do the conversion with the exception of the tape dope for the thermowell. Total time start to finish was a little over an hour. The pid seems to regulate the temp much better than the old AKO controller. The temp goes back and forth between 199 and 200. The set point is 200. I have noticed that the light that shows when the pid is calling for heat is not steady, it's on and off. I'm pretty sure that helps with temp overshoot and under temp conditions. ymmv
Herman

On Thu, Jan 21, 2016 at 2:29 PM, Schindler <[email protected] <mailto:[email protected]>> wrote:

    The USA distributor of AKO controllers can help with any questions
    http://schindlertechnologies.com/

    On Thursday, May 5, 2005 at 10:46:25 AM UTC-5, Doug Shannon wrote:

        AKO's New Temperature Controller

        First, I have to thank Sean for the hours he has spent on the
        phone
        with me discussing and guiding me through this process. If it
        wasn't
        for him, none of this would have been possible.

        Description:

        AKO's newest controller (model 14725) is capable of displaying
        3 digits
        in degrees F up to 999F. Temperatures below 100F can be
        displayed in
        tenths of a degree resolution. This enables the user to set
        the all
        important offset parameter in tenths of a degree. The new
        controller
        accepts a J or K type thermocouple allowing for faster
        response times
        as compared to the stock controller RTD type sensor.

        The size of the controller (due to having 3 digits) is
        slightly larger
        than the stock controller which will require a somewhat bigger
        panel
        cut out. Although tedious, the current cut out can be made the
        correct
        size with the use of a dremel tool. The width of the current
        cut out
        needs to be 1/2 in. wider and the height needs to be increased
        by 1/8
        in. There are no depth issues.

        You can see a picture of the 14725 on the brewtus group under user
        folders/Doug.

        Programming and Connections:

        I connected a common household extension cord to the power
        terminal of
        the controller. This allowed me to take my time programming the
        controller without fear of it affecting the operation of the
        brewtus.
        Once the controller was programmed which was a simple process
        by the
        way, I connected it to the brewtus using the same wires used
        to connect
        the stock controller. There are a total of 4 wires (power, sensor,
        relay, and common). As recommended by Sean, I used a 30 ga. K type
        sensor installed in the brew boiler's thermo well along side
        the stock
        sensor in order to hold it in place. As compared to the RTD stock
        sensor, the K type has greater accuracy and much faster response.
        Finally, I temporarily installed another sensor in the thermo
        well so
        that, using my Fluke 54, I could test the accuracy and
        response of the
        new controller.

        Initial Testing Results:

        After all connections were made and verified I plugged the
        brewtus'
        power cable into the wall, took a deep breath, and flipped the
        power
        switch with my barely controllable trembling hand. At this
        point, I had
        Sean on the phone who was intently listening for explosions
        and looking
        south outside his office window for mushroom clouds.
        Thankfully, there
        were none. The controller powered up and called for heat. Once the
        steam boiler reached 1.2 bar the temperature display began
        it's rise.
         Once it reached my set point of 203F, the heat light went
        out. But, oh
        no, the temperature display kept rising! The fluke display
        kept rising
        matching the readings from the controller. What could be
        wrong? The
        stock controller never rises above the set point! There must be
        something wrong with the controller,  I thought. I certainly
        didn't
        program it incorrectly and if I did it would have been Sean's
        fault,
        not mine (hehe).  After verifying the programming was correct and
        apologizing to Sean we decided to re-connect the stock
        controller and
        compare it's readings to that of the fluke. Our eyes were
        opened! The
        stock controller display would dip to 94 causing a call for
        heat. At
        this time, the fluke read 94C and then started to climb back
        to 95C as
        it should but alas, it kept rising all the way to 99C. That's
        an 8F
        temperature swing within the boiler but the stock controller's
        display never rose above 95C! Based on this information, we
        suspect
        that AKO specially programmed the stock controller for Expobar
        so that
        it would never show readings above the set point which gives the
        impression that the controller is doing a much better job at
        controlling boiler temperature than it really is.  The new
        controller
        doesn't do this. It truly shows the actual temperature,
        whatever it
        may be.

        After watching many heating/cooling cycles on the stock
        controller and
        determining there is on average an 8F swing in boiler
        temperature, I
        re-connected the new controller and continued testing. Upon
        watching
        numerous heating/cooling cycles, I determined that, on average
        it was
        able to control boiler temperature to within a 4.5F range - ½ that
        of the stock controller.  I believe this is due to the
        difference in
        resolution between degrees F and degrees C as well as better
        electronics, faster probes, and the ability to set offset in
        tenths of
        a degree.

        How did all of this affect brew temperature variance and average?
        Here's a comparison between the two controllers. First, let me
        outline the testing parameters:

        Warm Up Time: 2 hours
        Tested only 1st shot of the day (this is because I only brew
        one shot
        in the morning then one at night)
        Coffee used: vivace vita
        Shot volume: 1.5 oz.
        Shot time: 25-30 sec.
        Tamp pressure: 40lbs.
        Flush routine: 1.5 oz. flush, 1 minute to dose/tamp, 1.5 oz.
        flush,
        immediately pull shot.
        Target Brew Temp: 203F

        Stock Controller:

        Brew Temperature Variance: 1.2F (readings taken from the 10
        sec. on as
        per Schomer)
        Average Brew Temp off target: +- .8F

        New Controller:

        Brew Temperature Variance: .7F (readings taken from the 10
        sec. on as
        per Schomer)
        Average Brew Temp off target: +- .2F

        picture of a brew temp graph for the new controller is
        available on the
        brewtus group under user folders/Doug

        It should be noted that the time in which you start the shot
        within the
        heating/cooling cycle will greatly affect average brew
        temperature. If
        you start the shot just as the controller heats up to the set
        point you
        will get the results seen above.  However, if you start the
        shot during
        the cooling phase or just before the controller calls for
        heat, your
        average brew temperatures will be off as much as minus 2F.
        Unfortunately, this is the Achilles heel of these controllers.
        It would
take installing a PID controller to eliminate this problem. The AKO
        controllers are really just glorified thermostats. Their
        operation is
        analogous to a car approaching a stop sign at 60 MPH. It waits
        until it
        reaches the stop sign before applying the brakes causing sever
        overshoot whereas a PID controller is analogous to that same
        car gently
        applying the brakes as it approaches and actually stops at the
        stop
        sign. Sigh.

        In conclusion, I feel the new controller although falling way
        short of
        a PID controller, offers the following improvements over the stock
        controller:

        1. Displays 3 digit degrees F
        2. Faster more accurate readings and response time
        3. Ability to program offset in tenths of a degree
        4. Offers improved temperature stability

        Questions and comments are welcome. If enough people are
        interested we
        can put together a group buy. I will glady put together an
        installation
        manual for the group if there is enough interest.

-- You received this message because you are subscribed to the Google
    Groups "Brewtus" group.
    To unsubscribe from this group and stop receiving emails from it,
    send an email to [email protected]
    <mailto:[email protected]>.
    To post to this group, send email to [email protected]
    <mailto:[email protected]>.
    Visit this group at https://groups.google.com/group/brewtus.
    For more options, visit https://groups.google.com/d/optout.


--
You received this message because you are subscribed to the Google Groups "Brewtus" group. To unsubscribe from this group and stop receiving emails from it, send an email to [email protected] <mailto:[email protected]>. To post to this group, send email to [email protected] <mailto:[email protected]>.
Visit this group at https://groups.google.com/group/brewtus.
For more options, visit https://groups.google.com/d/optout.

--
You received this message because you are subscribed to the Google Groups 
"Brewtus" group.
To unsubscribe from this group and stop receiving emails from it, send an email 
to [email protected].
To post to this group, send email to [email protected].
Visit this group at https://groups.google.com/group/brewtus.
For more options, visit https://groups.google.com/d/optout.

Reply via email to