We have found a security exploit in the latest APC firmware versions for there 
switched rack PDU products. We have only tested this against the version listed 
below on a AP7932 0u 30amp PDU.


Name:   rpdu

Version:        v3.5.5

Date:   07/18/2007

Time:   11:38:29


Name:   aos

Version:        v3.5.6

Date:   07/18/2007

Time:   10:24:55

Date Reported to APC: 11-28-2007


Discovered by: 

Gary Simat of Total Server Solutions LLC

Randy Kent of Sevaa Group Inc


Steps to reproduce:

1) login to the APC as a user from computer 1

2) Then attempt to login from another computer (we will call this computer 2), 
the User Name and Password will not be editable, so just click Log On. It will 
say someone is already logged in. leave this page up.

3) logout of computer 1

4) simply hit refresh on computer 2 and select to resend the headers. you will 
be logged in as the previously authenticated user.

Reply via email to