All,

I read this post and there are comments that others have made that are 
dangerous.

Ground and Neutral shall NEVER be bonded on the load side of the main circuit 
disconnecting means.

Some are rather blasé about this.

If a generator has a “floating” neutral, it must be tied to the ground at the 
generator per the manufacturer’s instructions. You can test the connection with 
the generator powered OFF using an ohmmeter or powered on by a voltmeter. If 
you don’t know how to make this measurement, you shouldn’t mess with the 
generator.

In addition, the frame of the generator should be grounded to the earth or to 
some agree-upon grounding point that is grounded and this should be the sole 
source of earth connection.

The primary purpose of grounding is to ensure that you don’t become a “crispy 
critter” by touching something that is energized with respect to ground.

*

With switch-mode power supplies, there is a great deal of current flow on the 
neutral wire. Re-bonding on the load side causes a number of safety devices to 
not work properly.

73 and stay SAFE!

B
> On Apr 26, 2016, at 9:58 AM, Dwayne Jones via BVARC <[email protected]> wrote:
> 
> Good find Travis.
> 
> Dwayne
> KB5YTA
> 
> On Tue, Apr 26, 2016 at 9:49 AM, Travis Burgess via BVARC <[email protected] 
> <mailto:[email protected]>> wrote:
> 
> 
> This is from one of the portable ops groups:   
> http://noshockzone.org/generator-ground-neutral-bonding/ 
> <http://noshockzone.org/generator-ground-neutral-bonding/>\
> 
> 
> Travis
> 
> K5HTB
> 
> Generator Ground-Neutral Bonding | No~Shock~Zone 
> <http://noshockzone.org/generator-ground-neutral-bonding/>
> noshockzone.org <http://noshockzone.org/>
> I just read your article about creating a “Edison” plug for Ground-Neutral 
> bonding. The explanation was really clear for a layman like myself.
> 
> 
> _______________________________________________
> BVARC mailing list
> [email protected] <mailto:[email protected]>
> http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org 
> <http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org>
> 
> 
> _______________________________________________
> BVARC mailing list
> [email protected]
> http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org

Bill Crowell, N4HPG
Pearland, TX
[email protected] <mailto:[email protected]>
I prefer to live a life of galvanic isolation.