Robert, my shack ground rod is about 15 feet away from the house ground rod. 
Can I just run a heavy wire between the two as a good fix?

JP, K5JPP

>     On 05/23/2022 5:44 PM Robert Polinski via BVARC <bvarc@bvarc.org> wrote:
> 
> 
> 
>     My post only relates to if in fact you install a ground rod at your ham 
> station, that it needs and under the NEC is required to be bonded (connected) 
> to your house ground.  Lets assume your house ground rod has a résistance of 
> 22 ohms. You pound a rod at your shack in the earth that has a resistance   
> 10 ohms  Lightning strikes  your power line behind your house. This high 
> voltage pulse is seeking the least resistance path to earth. The house ground 
> not the best, but to the lightning Gods you shack ground looks like a great 
> path, using the 3rd prong of your power supply or the neutral side of the 
> power cord, it seeks that ground, kind of frying any wiring or equipment in 
> its travels. If both ground rods are bonded together, using ohms law, the 
> total resistance is 6.88 ohms, much better ground, lightning has a low 
> resistance path to earth not thru your gear.  Also from a safety aspect (why 
> the NEC requires bonding) if you loose a neutral connection at your power 
> drop to your meter, or in your breaker box and your house ground is missing 
> or poor, any grounded equipment in your house can have up to 120v on its 
> chassis. If you were touching equipment in your shack the was connected to 
> your shack ground and something grounded to your poor or non-existent house 
> ground. You will be a cooking hot dog. Robert
> 
> 
>     From: BVARC <bvarc-boun...@bvarc.org> On Behalf Of David Hold via BVARC
>     Sent: Monday, May 23, 2022 4:58 PM
>     To: BRAZOS VALLEY AMATEUR RADIO CLUB <bvarc@bvarc.org>
>     Cc: David Hold <davidh...@gmail.com>
>     Subject: Re: [BVARC] Ground rod
> 
> 
>     I will bet …. If you ohm out the negative post and chassis you will find 
> out they are the same.
> 
>      If so just take negative to ground rod or wire under a chassis screw to 
> ground.
> 
> 
>     On Mon, May 23, 2022 at 4:51 PM Mike Knedr via BVARC <bvarc@bvarc.org 
> mailto:bvarc@bvarc.org > wrote:
> 
>         > > 
> >         Thank you for the information.
> > 
> >         I have a semlex sec-1235m power supply.
> > 
> >         It doesn't seem to have a chassis ground like the radio and the 
> > tuner does.  Does it need to be grounded?
> > 
> > 
> >         On Mon, May 23, 2022, 1:53 PM Robert Polinski via BVARC 
> > <bvarc@bvarc.org mailto:bvarc@bvarc.org > wrote:
> > 
> >             > > > 
> > >             Do not preform any electrical work unless you are comfortable 
> > > as to what you are doing. Do not in any case ground the 3rd prong of an 
> > > electrical cord to a ground rod that is not bonded to your electrical 
> > > service. You could cause an electrical potential difference between 
> > > ground thru your equipment or thru YOU. Remember, an earth ground has 
> > > resistance. An electrical fault (short to chassis or ground) needs a low 
> > > resistance path back to its source, a metal conductor, the earth can be a 
> > > high resistance path. Low resistance will cause the protective device ( 
> > > Breaker or fuse) to open. Robert KD5YVQ
> > > 
> > > 
> > >             From: BVARC <bvarc-boun...@bvarc.org 
> > > mailto:bvarc-boun...@bvarc.org > On Behalf Of Joseph Benoit via BVARC
> > >             Sent: Sunday, May 22, 2022 8:59 AM
> > >             To: BRAZOS VALLEY AMATEUR RADIO CLUB <bvarc@bvarc.org 
> > > mailto:bvarc@bvarc.org >
> > >             Cc: Joseph Benoit <wa3...@gmail.com mailto:wa3...@gmail.com >
> > >             Subject: Re: [BVARC] Ground rod
> > > 
> > > 
> > >             Mike.  Not a direct answer to your ground rod issue BUT upon 
> > > inspection, you will find the wire feeding the outlet boxes probably does 
> > > contain a ground wire, just that they didn't have three-prong outlets or 
> > > continue grounds properly
> > > 
> > >             Not sure you want to tackle this BUT it is easy just 
> > > time-consuming. After you've done a couple, maybe 15 minutes each. 
> > > 
> > >             Experiment with one outlet to see if you are up to it.
> > > 
> > >             Look in your breaker panel and you will see a bunch of ground 
> > > wires connected to the ground buss so obviously they go SOMEWHERE (just 
> > > not terminated at the outlets and switches).
> > > 
> > >             Time to replace those old outlets and switches anyway.  Don't 
> > > buy the cheapest outlets, stick to made in USA; Proven to be better 
> > > connections inside.     
> > > 
> > >             You can fix the issue with the no-grounded outlets throughout 
> > > the house and make things much safer. Buy an outlet tester (a few bucks; 
> > > three LED's) if you don't have one.  Get about 10 feet (jic) #14 solid 
> > > copper wire green or whatever color.; stripping entirely bare if not 
> > > green. Have a small assortment of appropriate wire nuts and electrical 
> > > tape. Amazing how many three pronged outlets don't have any wire to 
> > > ground screw although the bare ground wire is in there (sometimes just 
> > > balled-up.  Good time to identify what breaker does what and to make sure 
> > > that breaker is OFF before you remove the outlet or light switch..  By 
> > > getting to each and every outlet and switch and make sure the ground 
> > > wires that are there are all connected to each other (may be multiple 
> > > cables in same box) connect them all together  adding a pig tail if it 
> > > was cut too short. Add a short pigtail to the new 3-prong grounded 
> > > receptacle. Also look at any junction boxes hiding in the attic.  Have to 
> > > be patient since, in an older house like ours, one room may feed another 
> > > room and the problem won't resolve until all the grounds are tied 
> > > together.  One day project does the whole house. 
> > > 
> > >             Good idea to take a wrap of tape around the receptacle or 
> > > switch for safety (for safety and to keep that ground wire from touching 
> > > where it shouldn't.  
> > > 
> > > 
> > >             On Fri, May 20, 2022 at 8:19 PM Mike Knedr via BVARC 
> > > <bvarc@bvarc.org mailto:bvarc@bvarc.org > wrote:
> > > 
> > >                 > > > > 
> > > >                 The house was built in the 60's.
> > > > 
> > > >                 So there is no ground to the receptacles.
> > > > 
> > > >                 I was planning on building an extension cord with a 
> > > > gfci and running the ground to the rod.
> > > > 
> > > >                 I was thinking about flat braid from a ground buss bar 
> > > > to the rod for the radio, tuner, and power supply.
> > > > 
> > > > 
> > > >                 Any thoughts?
> > > > 
> > > > 
> > > >                 Mike KI5UBL 73
> > > > 
> > > > 
> > > >                 On Fri, May 20, 2022, 7:57 PM Michael Giannaccio via 
> > > > BVARC <bvarc@bvarc.org mailto:bvarc@bvarc.org > wrote:
> > > > 
> > > >                     > > > > > 
> > > > >                     Hi Mike,
> > > > > 
> > > > >                     When I put mine in I left about 8-12” out of the 
> > > > > ground. Plenty of room for multiple clamps and coax grounding blocks.
> > > > > 
> > > > >                     If you’re not already aware make sure you bond 
> > > > > your station ground with your home’s electrical ground. I have some 
> > > > > wire that you’re welcome to for bonding if your run isn’t too long. 
> > > > > Let me know!
> > > > > 
> > > > >                     73,
> > > > > 
> > > > >                     Mike Giannaccio
> > > > >                     W5REZ
> > > > > 
> > > > >                     > On May 20, 2022, at 6:53 PM, Mike Knedr via 
> > > > > BVARC <bvarc@bvarc.org mailto:bvarc@bvarc.org > wrote:
> > > > >                     >
> > > > >                     >
> > > > >                     > I'm am installing an eight foot ground rod for 
> > > > > my new shack.
> > > > >                     > My question is how much leave above ground to 
> > > > > attach the grounds.
> > > > >                     > ________________________________________________
> > > > >                     > Brazos Valley Amateur Radio Club
> > > > >                     >
> > > > >                     > BVARC mailing list
> > > > >                     > BVARC@bvarc.org mailto:BVARC@bvarc.org
> > > > >                     > 
> > > > > http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
> > > > >                     > Publicly available archives are available here: 
> > > > > https://www.mail-archive.com/bvarc@bvarc.org/
> > > > > 
> > > > > 
> > > > >                     ________________________________________________
> > > > >                     Brazos Valley Amateur Radio Club
> > > > > 
> > > > >                     BVARC mailing list
> > > > >                     BVARC@bvarc.org mailto:BVARC@bvarc.org
> > > > >                     
> > > > > http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
> > > > >                     Publicly available archives are available here: 
> > > > > https://www.mail-archive.com/bvarc@bvarc.org/
> > > > > 
> > > > >                 > > > > 
> > > >                 ________________________________________________
> > > >                 Brazos Valley Amateur Radio Club
> > > > 
> > > >                 BVARC mailing list
> > > >                 BVARC@bvarc.org mailto:BVARC@bvarc.org
> > > >                 http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
> > > >                 Publicly available archives are available here: 
> > > > https://www.mail-archive.com/bvarc@bvarc.org/
> > > > 
> > > >             > > > 
> > >             ________________________________________________
> > >             Brazos Valley Amateur Radio Club
> > > 
> > >             BVARC mailing list
> > >             BVARC@bvarc.org mailto:BVARC@bvarc.org
> > >             http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
> > >             Publicly available archives are available here: 
> > > https://www.mail-archive.com/bvarc@bvarc.org/
> > > 
> > >         > > 
> >         ________________________________________________
> >         Brazos Valley Amateur Radio Club
> > 
> >         BVARC mailing list
> >         BVARC@bvarc.org mailto:BVARC@bvarc.org
> >         http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
> >         Publicly available archives are available here: 
> > https://www.mail-archive.com/bvarc@bvarc.org/
> > 
> >     > 
>     --
> 
>     David Hold david.h...@gmail.com mailto:david.h...@gmail.com
> 
>     ________________________________________________
>     Brazos Valley Amateur Radio Club
> 
>     BVARC mailing list
>     BVARC@bvarc.org
>     http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
>     Publicly available archives are available here: 
> https://www.mail-archive.com/bvarc@bvarc.org/
> 
________________________________________________
Brazos Valley Amateur Radio Club

BVARC mailing list
BVARC@bvarc.org
http://mail.bvarc.org/mailman/listinfo/bvarc_bvarc.org
Publicly available archives are available here: 
https://www.mail-archive.com/bvarc@bvarc.org/ 

Reply via email to