Sue asked:
> Will 10,000btu boiler heat two double radiators plus a calorifier. 
How 
> do I work out what size we need?
>

10,000 Btu *per hour*(note the difference) converts to 2.93 kW.
On my 59ft nb, spray foam insulated, I had a Mikuni MX40 to operate 
one large double rad, one medium single rad and a small bathroom 
towel rail style rad. It could also handle the calorifier coil as 
well, if required. The MX40 is rated at 4.8 kW max and 2.4 kW at half 
heat. It took about half an hour to start to get the boat warmer on a 
chilly day with the Mikuni and longer to really feel a significant 
benefit (running at 4.8 for the first half hour or so). We also would 
have had a Morso stove running on cold days.
I would think that 2.93 kW would take a while to heat up the boat 
but, once warm, might just about manage it (depending on external 
temperatures, boat insulation etc). Having said that though the 
Mikuni used to kick back into full power on really cold days so I 
suspect that 2.93 kW might be a little on the light side.

You could also try adapting room dimensions and other data in a site 
such as http://www.radcalcs.com/ to calculate your requirements but 
it is a bit of a bodge as you are using a house based calculator for 
boiler sizing.
Best I can do I'm afraid.