On Wed, May 22, 2019 at 3:50 AM Christian Corti via cctalk < [email protected]> wrote:
> On Tue, 21 May 2019, Patrick Finnegan wrote: > > Plumbing (unless you're doing aisle containment or RDHx) shouldn't run > > through the IT space in the data center. > > So how exactly do you attach a modern water cooled rack system to your > cooling water system if not using plumbing? > I guess I should have added "etc" to my exception list? My point was that air handlers, CRACs, etc, should not have their plumbing running through the data center since they should be outside in a mechanical room anyways. > > Cooling water to racks should be dewpoint adjusted, so you don't need > > condensate drains inside the DC. > > That is a requirement, you must have condensate drains just in case that > the room temperature and/or air humidity rises, or cooling water > temperature goes below the dew point. > For what we do, It's not, we don't do that, and our equipment suppliers don't suggest it. The air is humidity controlled before it gets near the IT racks, by building air handlers and CRAC units. Our process water loop inside the room watches the humidity and adjusts the water temperature appropriately. It'd be hard to for the dewpoint to change rapidly enough to cause condensation vs how quickly systems can increase the water temperature to compensate. Modern systems using direct-to-system water cooling also tend to use "warm water" cooling, since they don't need water below ~90F (~32C) to cool effectively (some specify up to ~104F (~40C). RIP the data center that has a dewpoint that high, since the servers will probably be covered in rust pretty quickly. Pat