For a 6509-V-E with 2xVS-S720-10G-3CXLs and 7xWS-X6708-10G-3CXL.Cisco Power Calculator shows:
107.76 Amps 4525.92 Watts 18183.55 BTU/Hr At 21u you could squeeze two in a rack, for 9K (we aren't planning on doing that though.) On the server side something like an HP C Class Blade Chassis with 16 blades can hit 3K when the fans rev up. At 10u you could squeeze 4 in a rack, but cooling is going to be an issue. With enclosed ducted racks, we currently have plans to put 3 in a rack for a total of 9K. So yes we could require >6K. Tim:> On Sat, Mar 22, 2008 at 10:02 PM, Patrick Giagnocavo <[EMAIL PROTECTED]> wrote: > > Hopefully this classifies as on-topic... > > I am discussing with some investors the possible setup of new datacenter > space. > > Obviously we want to be able to fill a rack, and in order to do so, we > need to provide enough power to each rack. > > Right now we are in spreadsheet mode evaluating different scenarios. > > Are there cases where more than 6000W per rack would be needed? > > (We are not worried about cooling due to the special circumstances of > the space.) > > Would someone pay extra for > 7KW in a rack? What would be the maximum > you could ever see yourself needing in order to power all 42U ? > > Cordially > > Patrick Giagnocavo > [EMAIL PROTECTED] > _______________________________________________ cisco-nsp mailing list [email protected] https://puck.nether.net/mailman/listinfo/cisco-nsp archive at http://puck.nether.net/pipermail/cisco-nsp/