There are two ABYC requirements for new boats- one being the GFCI
requirement ( 5mA trip specified  ) for the receptacles in wet areas and the
second being ELCI breakers on the shore power feed which typically have a
30mA trip. Both are required.

 

I installed the Blue Sea ELCI when I was updating my A/C side last year and
haven't had any nuisance trips. I have both charger/inverter and hot water
on the boat.

 

 

Ed

 

Prime Interest

1982 C&C 38 Landfall

Toronto, Canada

 

 

From: CnC-List [mailto:[email protected]] On Behalf Of Ken
Heaton
Sent: Tuesday, April 01, 2014 5:40 PM
To: cnc-list
Subject: Re: Stus-List GFCI Outlet

 

Hey Edd,

 

I wouldn't put one GFCI inline from the shore power.  It would need to be
large and expensive (2 pole, 30 amp) as you will end up running everything
through it including the heating element in the hot water heater and your
battery charger.  Also, many modern battery chargers may cause it to
nuisance trip frequently.

 

The GFCI in an outlet is cheap, effective and obvious if it trips as they
will usually have a small LED indicator on the face and only the circuit
that is tripped (and the outlets downstream) will go dead, not the whole
boat.  I think your boat has two breakers in the AC panel for the AC outlets
so you will only need two (or possibly three, depending on how the wire is
run) GFCI's to do the whole boat.

 

I think the level of safety these GFCI provide for very little money is
worth it.  I'm not sure how the ABYC requirement for all new boats is
written so I don't know if dong it this way will cover it.

 

Ken H.

 

As Dennis C. said:

 

"Look at the GFCI receptacle you are installing.  It should have two pairs
of hot/common connections and one ground.  One pair will be labeled "Line"
and one pair "Load".  The "Load" connections are protected.


The correct wiring should be from your supply (breaker) to the pair marked
"Line".  Downstream receptacles should be wired from the "Load" pair.

Also, make sure you get the black (hot) and white (common or neutral) wires
on the correct connectors for all connections.

 

Dennis C."

 

On 1 April 2014 14:08, Edd Schillay <[email protected]> wrote:

Listers,

 

Thanks to the wisdom of the group, I'm redoing the entire AC system of the
Enterprise, including a switch from shore power to inverter. If you listen
carefully, you'll hear a stream of cursing coming from City Island this
weekend as I try to squeeze myself into yoga-expert positions trying to
snake wires.  

 

As to a GFCI outlet, is it best to put it first in the line of outlets or
last? Or does it not matter? 

 

Would it make sense to just install a GFCI inline from the shore power
instead? 

 

All the best,

 

Edd

 

 

Edd M. Schillay

Starship Enterprise

C&C 37+ | Sail No: NCC-1701-B

City Island, NY 

Starship Enterprise's Captain's Log <http://enterpriseb.blogspot.com/> 

 