JonasH-munters commented on PR #2251:
URL: https://github.com/apache/plc4x/pull/2251#issuecomment-3281485250

   Thank you for the response and I definitely think I might be one of the 
confused ones so any clarifications that can be done on the PLC4X API level as 
a result of this PR will be great I think :D Just gotta figure out the best 
clarifications to do!
   
   What you say makes sense for cyclic subscriptions so maybe removing the 
`addCyclicTag` and `addCyclicTagAddress` methods with a `consumer` parameter 
from the `DefualtPlcSubscriptionRequest.Builder` class would make sense? Or 
some other way of reducing user confusion compared to the current state where 
the consumers are just ignored. But I was under the impression that for the 
`PlcSubscriptionType.CHANGE_OF_STATE` ones that I'm using the plc event only 
contains the ones that actually had their values change. When I debug with a 
breakpoint in the `OpcuaSubscriptionHandle` class I can see that the 
`DataChangeNotification` object that I receive most of the time contains only 
18 values of 74 tags I subscribed to in my test case. Is that not how OPC UA 
change of state subscriptions should work? If not, maybe it could be relevant 
to support anyway since it seems at least the server I'm using (Kepware) 
behaves that way?


-- 