kostinkirill commented on PR #2336:
URL: https://github.com/apache/plc4x/pull/2336#issuecomment-3515822211

   > I assume the next step would be to extend the ADS and possibly the OPC-UA 
driver to support this, right? Are you planning on continuing to work on this? 
I's prefer to mentor you through this as it's a bit like the "give a man a fish 
and he's fed for a day, teach him to fish and he's fed for life" sort of thing 
;-)
   
   I believe ADS drive already supports it, I've already checked the behavior 
and `minInterval` is applied for CHANGE_ON_EVENT subscriptions and works as 
epxected. 
   This the code where the `minInterval` is set up as `cycleTimeInMs` in 
`AdsAddDeviceNotificationRequest`
   `AdsProtocolLogic#executeSubscribe:
   ```
   return new AmsTCPPacket(new 
AdsAddDeviceNotificationRequest(configuration.getTargetAmsNetId(), 
configuration.getTargetAmsPort(),
                       configuration.getSourceAmsNetId(), 
configuration.getSourceAmsPort(),
                       0, getInvokeId(),
                       directAdsTag.getIndexGroup(),
                       directAdsTag.getIndexOffset(),
                       adsDataTypeTableEntry.getSize() * numberOfElements,
                       tag.getPlcSubscriptionType() == 
PlcSubscriptionType.CYCLIC ? AdsTransMode.CYCLIC : AdsTransMode.ON_CHANGE, // 
if it's not cyclic, it's on change or event
                       0, // there is no api for that yet
                       tag.getDuration().orElse(Duration.ZERO).toMillis()));
   ```
   (the last argument)
   
   As for OPCUA, I haven't checked it, but based on the code it should work as 
well
   


-- 