   ## Summary
   
   Replaces the per-connection NIO `Selector` in `TcpTransportInstance` with 
one virtual thread per
   connection doing **blocking** `SocketChannel.read()` / `write()`. Stays 
fully Netty-free. Follows the
   SPI3 transport layer (commit `372501287d`); @chrisdutz greenlit a redesign 
of this transport and
   offered bench testing on real devices — this is that redesign, TCP-only as a 
first step.
   
   Scope is confined to `plc4j/transports/tcp` (`TcpTransportInstance`). **No 
public API / SPI / driver
   changes.**
   
   ## Motivation (verified against current code)
   
   1. **A vthread blocked in `Selector.select()` does not release its carrier 
on Java 21.** Two reasons:
      (a) pre-JEP-491 the selection path synchronizes on the selector monitor 
(a monitor pin, fixed in
      JDK 24); and (b) more fundamentally, `select()`'s native poll is **not** 
a carrier-unmounting /
      poller-managed operation, so the carrier stays blocked **even after JEP 
491**. The scheduler
      compensates up to `maxPoolSize` (default 256) → we pay vthread overhead 
but get platform-thread
      behavior plus a hidden ~256 ceiling, and this does not improve on newer 
JDKs.
   2. **Write backpressure is a busy-wait:** on a full send buffer, `write()` 
registers `OP_WRITE`,
      `wakeup()`s, then `Thread.sleep(1)` in a loop while holding `writeLock` 
(never consumes the event).
   3. **Selector + per-connection bookkeeping** (`interestOps`, 
`reEnableReadIfNeeded`, OP_READ toggling).
   
   On Java 21 a vthread blocked in a **blocking-mode** 
`SocketChannel.read()`/`write()` parks and
   **releases its carrier** (JDK parks it on the shared NIO poller) — no pin. 
So one-vthread-per-connection
   blocking reads is both simpler and avoids the ceiling.
   
   ## What changed
   - `select()` loop → `runReadLoop()` doing blocking `read()` into the 
existing `RingBuffer`.
   - Removed `Selector`, `SelectionKey`, `interestOps`, `reEnableReadIfNeeded`, 
and the `OP_WRITE` +
     `Thread.sleep(1)` write path. Blocking `write()` now provides natural 
backpressure.
   - Full ring buffer → **backpressure** (`parkNanos` park-and-retry, bounded 
to free space), never a
     disconnect (only the codec knows frame boundaries; COTP can legitimately 
drain cross-thread).
   - `close()` is lock-free CAS (`AtomicBoolean`): closing the channel is what 
unblocks a parked
     read/write; `AsynchronousCloseException` with `open==false` is treated as 
a normal shutdown.
   - Listener invocation guarded (`safeRun`) so a misbehaving listener can't 
silently kill the read loop.
   
   ## Zero downstream impact (audited)
   Public surface, `readLock`, `RingBuffer`, and the `AsyncTransportInstance` 
callback contract are
   **unchanged**. `readLock` is deliberately kept because 
`CotpTransportInstance` calls the read-side
   methods **cross-thread** during the S7/COTP handshake — it is a load-bearing 
guard, not removable.
   
   | Consumer | Affected? |
   |---|---|
   | `MessageCodecBase` + driver codecs (read-thread) | No — contract/semantics 
preserved |
   | `ConnectionBase.startReceiving` (`registerDataListener`) | No — read 
vthread invokes the listener exactly as the selector loop did |
   | `CotpTransportInstance` (cross-thread read-side, concurrent) | No — 
`readLock` + read-side thread-safety preserved |
   | `OpcuaConnection` (`instanceof` + `getRemoteAddress`) | No — concrete 
class + surface preserved |
   
   ## Evidence
   - **`TcpTransportInstanceTest` (31 tests) passes unmodified** on the new 
implementation → behavior-equivalent.
   - **Scaling — carrier (OS) threads for 200 idle connections (measured; 
`@Disabled` probe, run manually):**
   
     | model | JDK 21 | JDK 25 |
     |---|---|---|
     | selector (before) | 201 | 201 |
     | blocking (after)  | 2–3 | 2–3 |
   
     The selector inflates to ~1 carrier per connection on **both** JDKs, so 
JEP 491 (JDK 24, removes
     `synchronized` pinning) does not help here — the cost is `select()` being 
a non-unmounting blocking
     call, not monitor pinning. The blocking model stays flat (bounded by CPU 
count, not connection
     count), so the win does not erode as Java advances. (All four cells 
reproduced with the same probe:
     selector `CARRIER_COUNT=201` and blocking `CARRIER_COUNT=2` for 200 
connections, on JDK 21 **and**
     JDK 25; no pinned-thread traces for the blocking model under 
`-Djdk.tracePinnedThreads=full`.)
   - **End-to-end regression:** `ModbusDockerIT` (pymodbus container) — all 
cases green. The
     `modbus-tcp://`, `modbus-rtu:tcp://`, and `modbus-ascii:tcp://` cases 
(~38) exercise the new
     `TcpTransportInstance` over a real socket; the UDP and TLS cases use the 
separate UDP / TLS
     transports and are unaffected by this change.
   
   ## Scope / non-goals
   - TCP only. UDP (shares the selector pattern) is the natural follow-up; 
serial/TLS already use
     different reader-thread models.
   - No SPI contract reshape. The `AsyncTransportInstance` callback is 
intentionally kept as a thin shim
     on the blocking core; migrating to a blocking-pull contract is 
**intentionally out of scope**.
   
   ## Testing notes
   - `TcpTransportInstanceScalingTest` is an `@Disabled` evidence probe (opens 
200 sockets + sleeps; not a
     CI regression test) — run manually, ideally with 
`-Djdk.tracePinnedThreads=full`.
   - `mvn -pl :plc4j-transports-tcp -am verify` is green (tests + apache-rat + 
jacoco).
   - Bench validation on real devices welcome, as offered.
   


-- 