This is an automated email from the ASF dual-hosted git repository.

sruehl pushed a commit to branch develop
in repository https://gitbox.apache.org/repos/asf/plc4x.git

commit 69f65244fa33bbfa4cbf90873166aed6c9a33713
Author: Sebastian Rühl <[email protected]>
AuthorDate: Mon Jul 20 13:58:10 2026 +0200

    fix(plc4go): defaultCodec.Connect started workers before running=true - 
worker could die at startup
    
    A worker goroutine that got scheduled between startWorkers() and
    running.Store(true) observed running==false twice - in its mainLoop
    condition and in its restart defer - and terminated permanently while
    Connect still returned success. A codec without its expire worker never
    times out expectations, so SendRequest callers waiting on handleError
    hang forever. This is what intermittently wedged
    TestReader_sendMessageOverTheWire (internal/cbus) under -race: the
    timeout dump shows a live ReceiveWork but no ExpireWork goroutine.
    
    Store running=true before starting the workers; the goroutine-creation
    happens-before edge then guarantees both workers observe true.
    
    Falsification test probes worker liveness after Connect via a blocking
    send on the unbuffered notify channels (received iff a worker sits in
    its select). Verified RED first: expire worker died within ~5 of 1000
    iterations pre-fix; 5000 iterations green post-fix, and the cbus test
    survives 30 -race iterations (previously hung within 10).
---
 plc4go/spi/default/DefaultCodec.go      |  6 ++++-
 plc4go/spi/default/DefaultCodec_test.go | 43 +++++++++++++++++++++++++++++++++
 2 files changed, 48 insertions(+), 1 deletion(-)

diff --git a/plc4go/spi/default/DefaultCodec.go 
b/plc4go/spi/default/DefaultCodec.go
index be59bcb655..e1d7ad4cb6 100644
--- a/plc4go/spi/default/DefaultCodec.go
+++ b/plc4go/spi/default/DefaultCodec.go
@@ -171,8 +171,12 @@ func (m *defaultCodec) Connect(ctx context.Context) error {
        }
 
        m.log.Debug().Msg("Message codec currently not running, starting worker 
now")
-       m.startWorkers()
+       // running must be true BEFORE the workers start: a worker that observes
+       // running==false in its loop condition AND in its restart defer 
terminates
+       // permanently, leaving a "connected" codec whose expectations never 
expire.
+       // The goroutine-creation happens-before edge guarantees the workers 
see true.
        m.running.Store(true)
+       m.startWorkers()
        m.log.Trace().Msg("connected")
        return nil
 }
diff --git a/plc4go/spi/default/DefaultCodec_test.go 
b/plc4go/spi/default/DefaultCodec_test.go
index d5906085c4..e85ff31b0a 100644
--- a/plc4go/spi/default/DefaultCodec_test.go
+++ b/plc4go/spi/default/DefaultCodec_test.go
@@ -438,6 +438,49 @@ func Test_defaultCodec_Connect(t *testing.T) {
        }
 }
 
+// Test_defaultCodec_Connect_workersAliveAfterConnect is a falsification test
+// for the worker-startup race: Connect used to start the workers BEFORE
+// running.Store(true), so a worker observing running==false in both its loop
+// condition and its restart defer terminated permanently — leaving a
+// successfully "connected" codec whose expectations never expire and whose
+// messages are never received (observed as an infinite hang in the cbus
+// Reader tests). An idle worker blocks in its select receiving from its
+// (unbuffered) notify channel, so a blocking send succeeds iff the worker is
+// alive.
+func Test_defaultCodec_Connect_workersAliveAfterConnect(t *testing.T) {
+       for i := 0; i < 1000; i++ {
+               requirements := NewMockDefaultCodecRequirements(t)
+               requirements.EXPECT().Receive(mock.Anything).Return(nil, 
nil).Maybe()
+               instance := NewMockTransportInstance(t)
+               instance.EXPECT().IsConnected().Return(true)
+               instance.EXPECT().Close().Return(nil)
+               // A receive cycle in flight during Disconnect classifies the 
synthetic
+               // "not running" error before the worker notices the shutdown.
+               
instance.EXPECT().ClassifyError(mock.Anything).Return(transports.TransportErrorTransient).Maybe()
+               codec := buildDefaultCodec(requirements, instance, 
options.WithCustomLogger(testutils.ProduceTestingLogger(t))).(*defaultCodec)
+               require.NoError(t, codec.Connect(testutils.TestContext(t)))
+               t.Cleanup(func() {
+                       if codec.IsRunning() {
+                               _ = codec.Disconnect()
+                       }
+               })
+               for _, probe := range []struct {
+                       worker string
+                       notify chan struct{}
+               }{
+                       {"expire", codec.notifyExpireWorker},
+                       {"receive", codec.notifyReceiveWorker},
+               } {
+                       select {
+                       case probe.notify <- struct{}{}:
+                       case <-time.After(5 * time.Second):
+                               t.Fatalf("iteration %d: %s worker died during 
Connect", i, probe.worker)
+                       }
+               }
+               require.NoError(t, codec.Disconnect())
+       }
+}
+
 func Test_defaultCodec_Disconnect(t *testing.T) {