Mike

I think you will find that only a tiny airflow is needed for humidity and temperature control, as long as the need for heating or cooling is minimal. Cooling a showcase when the temperature differential between gallery and showcase is more than a few degrees needs much more air flow through the showcase, and there can be a danger to objects, so louver design and air path must be very carefully designed.

Some years ago, I entertained myself by performing a number of "kitchen sink" experiments on the effect of very low airflow/volume air flows in sealed showcases. Where necessary I used air containing smoke particles so that I could photograph and record air movement, but I also used sensors to record temperature differentials that resulted from air movement.

One of this series of experiments used an extremely small blower (about 5mm X 25mm X 25mm, for computer component cooling) that I further choked down to create an airflow that was only perceptible by pointing the device at my eyeball and feeling the need to blink. Needless to say, the flow was quite small, and beyond my ability to quantify.

For the experiment, I used a very small, and very well gasketed cast metal enclosure, with a large glass window. I placed one thermocouple free in the air near the top of the chamber, and the other near the bottom. I then used a small incandescent bulb located outside the window to create a temperature stratification of 2 deg C between top and bottom sensors.

This arrangement proved to be quite stable, until the miniature blower was energised. The temperature differential disappeared within a few minutes!

I suggest you try a similar test, using a small aquarium pump (similar to the Mini One humidity control devices) and a few data loggers. Please let me know how this works out, especially as you vary your air flows and case sizes. If you would like to discuss cooling optios, please contact me off-list.

js

We are currently working on a display case design with circulating air flow to ensure temperature and humidity is consistent around the case. We are looking for guidance on acceptable airflow rate that should be used to ensure there is no harm to objects. Does anyone have any experience or know of any guidelines in this area?

Many thanks

--
Jerry Shiner
Keepsafe Microclimate Systems
www.keepsafe.ca   [email protected]
+1 416 703 4696    +1 800 683 4696
skype: jerry.shiner

******
Unsubscribe by sending a message to [email protected]
Searchable archives: http://cool.conservation-us.org/byform/mailing-lists/cdl/

Reply via email to