glcj commented on issue #702:
URL: https://github.com/apache/plc4x/issues/702#issuecomment-1407487275

   Hello,
   
   In the captures (pcap) you can clearly see that the problem is in the PLCSIM 
response, specifically the length of the "Data.Item" is 32, when it should be 4 
(the length of a real in bytes).
   
   The request job is correct byte for byte, relative to my local test.
   
   The value of 32 would be valid if the "Transport size" were in bits.
   
   For the moment I must point out that the problem is in the PLCSIM.
   
   I did the test with version 4.0 of PLCSIM, please, if you can download and 
try with this version, you have a 15-day trial license.
   
   I will be careful,
   Best regards,


-- 