Hi all,

Just to update you all on this:

1. The host was running several other disk-intensive VMs. We shut them down.
2.  I reduced the MaxClients to a much lower value.
3.  I also set the swappiness=0 on both the host and the vm

We ran some load tests on it, both before and after these changes to confirm that they were helping.

What apparently happened was that MaxClients was too high. The system got hit with a very large load, and it hit maxclients. Swapping may also have been going on.

It has been in production since Wednesday and has performed very nicely.

Thanks again to all of you who responded.


JBB

On 10/18/2012 8:53 PM, Aleksey Tsalolikhin wrote:
On Mon, Oct 15, 2012 at 8:01 AM, Jonathan Bayer
<[email protected]> wrote:
The problem is that when the req/sec starts to climb on the VM, all of a
sudden the load average skyrockets to 40-50 or even higher. This kills the
server and makes it totally unresponsive.

Anybody have any suggestions?
What does "vmstat 1" show when the load starts to climb?  I suspect
you are swapping,
in which case your "si" and "so" (swap in and swap out) columns will
be non-zero.

If so, the solution would be to increase RAM per VM instance, or add
more instances to
distribute the work more.  (To shrink each VM's share of the workload.)