I have spent a lot of time researching surge suppression as it is a real
problem I have run into lately.

You didn't say what you're using now but one of the most effective
solutions for whole-home protection is to get a "TVSS" module that is
designed for your panel(s) and fits in the space of a dual-pole breaker
(for example, here's one for a Square D Homeline panel:
http://tinyurl.com/ydq736z ). These must be positioned only in the
top-left or top-right slots to be maximally effective, so you will
probably need to move all the other breakers down two spaces - usually
that is not a big deal.  These devices have LEDs on them which you
should check every few months to make sure they're alive - if you are
getting surges and they're doing their job, they will eventually
expire.

The only thing better than that is an large external TVSS **BUT** this
will only be an improvement if you actually route the main feed THROUGH
this device - and for that to work it must be rated for passthrough
current equal to the main disconnect feeding it. If you are on 200A
service then it's probably not practical.

The reason wiring distances come into play is that a lightning strike
is an RF signal because of the rapid rise of the voltage. Every foot of
cable between your breaker panel and the TVSS results in about 150V of
reduced clamping voltage. You you can still get some benefit from a
"dangling" TVSS, but not as much as putting them right in the path of
the surge.

If you have already put TVSS devices on your main/sub panels then
you're probably already at the point of diminishing returns there as far
as >500V suge events are concerned. 

This still leaves brownouts and lower, longer duration overvoltages.
These may not be a problem for you but they can be prevented by putting
your most expensive equipment on good quality UPSes.

Finally, your phone lines (and cable TV, if it's an aerial feed) are a
very likely vectors for surges to enter the house but usually these only
threaten the modems or data interfaces in the particular devices to
which they're connected. APC makes a MOV-based device, but there is a
new product from ELK which more sophisticated and supposedly better
(http://www.smarthome.com/1298/Elk-ELK-952-In-Line-Telephone-Surge-Protector/p.aspx).
That product is made for alarm panels - I don't know if it is OK for
modem/fax/DSL. It is very important with these devices that they have a
good ground connection - but also that the ground connection is close to
the device being protected. You can put one in your phone box but it
would be best to put them individually at your alarm panel, DVR, etc.


-- 
seanadams
------------------------------------------------------------------------
seanadams's Profile: http://forums.slimdevices.com/member.php?userid=3
View this thread: http://forums.slimdevices.com/showthread.php?t=73008