[email protected] writes:
> I've seen top tier brand servers with redundant power supplies shut down 
> because the power supply system inside the computer flaked out and decided 
> that both power inputs were bad (disabling both power supplies)
> 
> I've seen rats in the wall chew into power lines, shorting them out and 
> downing the system.
> 
> I've seen UPS systems that were reviewed by the maintinance company a week 
> prior fail to handle a loss of power and shut everything down


The vast majority of data center power failures I have seen were do to 
people, either through greed, ignorance, or inattention, overloading
a circuit.  

I've done it myself;  once, when I was much younger and less experienced
than I am now.   the thing most people don't realize is that not only 
does power draw change based on load, it changes based on temperature, too.

Of course, this is pure incompetence, but still, I'm sure, the #1 killer
of power in data centers.   The problem is that most places charge per
circuit, so the business types want to use as much of each circuit as they 
can.   It seems like it would encourage more rational decisions if 
power was metered.  

And those redundant power supplies.  People get them, plug 'em into 
different circuits, but then they load each circuit beyond 50%.  One 
of the circuits dies, and blam, of course the other one immediately 
blows as well.  It's not like they use half the power when one power 
supply dies.  