Rob Cherry wrote:
> I am working on a brand new IT room for around 4 high (12kw?) power
> racks and 2 wiring racks.  I was talking to the obvious choice -
> Liebert - and they came back with a fairly eye watering quote that
> made me question whether they are the only game in town.  During my
> research I fell across two companies - Rittal for cooling and Rittal's
> rebadge of Eaton technologies Powerware line of UPSes.

When I last did this, I used Rittal racks, but a Liebert Data-Pad, which is 
(was) a raised floor made of 2-by-4 modules a foot deep, including a couple of 
fan-coil units inside the floor.  The floor was a pressurized plenum, and the 
racks (Rittal NEMA-12 dust-tight, though hardly necessary) had open bottoms 
over 
cut tiles, and fans sucking air out the top.

Each rack was a separate, balanced-draft flue, in fact.  3-ton Liebert process 
chiller on the roof; nice, big, professionally-installed copper pipe down the 
corner.  And it wasn't cheap.  But the room was so small, nothing else would 
fit.

Before: Some servers were too hot to touch, no exaggeration.  After: Cold as 
corpses.

Given that racks are designed more for front-to-back airflow these days, you'd 
have to have them pretty deep to play this game, a bit more than 30 inches I'd 
guess.  And of course not with mesh doors.  But damn, it worked well.