On 5/9/2013 11:57 AM, Don Wilhelm wrote:
Option 2 only.
In fact, if you want to make it even better, run a #6 copper wire all around the perimeter of the house with a driven ground rod anywhere it makes a turn more than 30 degrees. That perimeter wire provides a path for lightning instead of allowing it to punch a hole in your building foundation.

I would also suggest at least 3 radial wires from the tower (length at least 1/2 the tower height) with driven ground rods spaced twice the length of the ground rod.

I like this advice, BUT -- also make sure that ALL other grounds are also bonded to this ground. That includes the common connection of all the gear in your shack (which should have a bond from one chassis to another for each piece of gear), the antenna entry point, cable TV system, telephone system, cold water (it it's metallic), structural steel if there is any, and the green wires for all the outlets in your shack.

A quibble though -- the "green wires" for all the outlets must be bonded to the enclosure of the main breaker panel, and they MUST be connected to your gear via the power cord. That combination of wires IS a connection through the house, although it's not a very good one, both because the conductors are small and they're long, so they're inductive. SO -- my advice, and what I've done in MY shack (where power is on one side of the building and the shack is on the other), is to do BOTH the perimeter wire (#4) with rods at multiple points along the run, and bonding the steel conduit (EMT) that carries wiring for the shack to the operating desk common point, and to the coax entry point.

The fundamental concept is that you want to provide a robust, short path to earth for the strike (which can come in on your antennas, the tower, a phone line, a CATV cable, the power line, and even the wiring inside your home), and for everything in your premises to stay as close to the same potential as possible. To accomplish that, you want multiple paths to earth (ideally close to every entry point), and the lowest possible IMPEDANCE between everything in the premises, with conductors large enough that they can carry as much current as practical before they melt. :) Because lightning is an RF event, with a very broad energy peak around 1 MHz, the impedance is mainly INDUCTANCE, not resistance, which is why "short" matters, and why more parallel inductors are better than one.

73, Jim K9YC
______________________________________________________________
Elecraft mailing list
Home: http://mailman.qth.net/mailman/listinfo/elecraft
Help: http://mailman.qth.net/mmfaq.htm
Post: mailto:[email protected]

This list hosted by: http://www.qsl.net
Please help support this email list: http://www.qsl.net/donate.html

Reply via email to