On 7/9/2018 11:29 AM, Josh Fiden wrote:
I take what code requires as the minimum wire gauge. For shorter runs it's 
fine. But measure the run length, multiply by 2 (two wires) and calculate IR 
voltage drop.

Actually, the voltage drop is greater than you calculate with the simple formula because current to electronic loads is not a sine wave!  This makes Josh's advice even better!  There's a technical discussion of this in  http://k9yc.com/GroundingAndAudio.pdf beginning around slide #56.

It's not a big expense when you're installing to use 10 instead of 12 awg if it 
would make a noticeable difference.

Yes. The cost of that outlet is mainly labor. I would even consider #10 small if it's a very long run, and consider #8. And our advice is not specific to the KPA1500 -- it would be the same for any big electrical load.

73, Jim K9YC